Aluminum SER? OK or Not #49637
03/11/05 07:01 PM
03/11/05 07:01 PM
T
tsolanto  Offline OP
Member
Joined: Sep 2002
Posts: 131
Long Island NY
Can't get a straight answer on this one it seems like so many people use rules of thumb or take what someone else told them as "the code" . I have an 86 meter service to install in an apartment. all the meters are in the basement along with the main switch. All of the apartments are fed with sub panels. I would like to feed them with Aluminum SER. Inspector says we must use copper after the main switch. I cant find that in the NEC or the NYS residential code. Any thoughts. What do you do in your state???

Work Gear for Electricians and the Trades
Re: Aluminum SER? OK or Not #49638
03/11/05 07:52 PM
03/11/05 07:52 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA
A couple of our municipal codes in So CA:

  • No Aluminum at all (mostly near the ocean)
  • No Aluminum #6 or smaller
  • No Aluminum #4 or smaller

Re: Aluminum SER? OK or Not #49639
03/11/05 08:01 PM
03/11/05 08:01 PM
T
tsolanto  Offline OP
Member
Joined: Sep 2002
Posts: 131
Long Island NY
Is there anything anywhere that says NO AL after the main switch? Remember I'm in NY Long Island.. crazy place

Re: Aluminum SER? OK or Not #49640
03/11/05 08:52 PM
03/11/05 08:52 PM
H
highvoltageguy  Offline
Member
Joined: Mar 2005
Posts: 53
Silt, Colorado, USA
I did copper on first few houses I did (Meter to Main) thinking I was doing quality stuff finally the inspector told me use the alum. and it's ok 310.15(b)(6) like every one else does make pocket some more money for myself. and the code says AL. service entrance cable is ok but if your inspector says no alum. after main, thats the way it is, no arguing with the MAN. the only place I would even consider Alum. is for a elec. Range but never have, guess I'll go look that up right now if really could.

Re: Aluminum SER? OK or Not #49641
03/11/05 09:11 PM
03/11/05 09:11 PM
R
Redogs54  Offline
Junior Member
Joined: Mar 2005
Posts: 8
Charlotte, NC, USA
Here in North Carolina we can use aluminum for the service connections as well as heavy loads such as A/C sub-panels, ranges, dryers and so forth. I did an apartment complex in Charleston, South Carolina and the local juristiction says no aluminum in any building. Must be a local ruling in your area.

Re: Aluminum SER? OK or Not #49642
03/11/05 09:14 PM
03/11/05 09:14 PM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
Unless your inspector can show you a local amendment to the NEC, I think he's wrong.(310.2)(310.5)(310.14)
We have a local amendment not allowing Alluminum, that dates back to when alluminum was burning up at terminations.

Re: Aluminum SER? OK or Not #49643
03/12/05 07:22 AM
03/12/05 07:22 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Quote
but if your inspector says no alum. after main, thats the way it is, no arguing with the MAN.
Can the MAN make it rain and snow too? [Linked Image] In MA we have rules. They apply to everyone, even the inspectors. Here, if it does not exist in writing and has not been adopted into law, it is not an enforcable rule. Don't just roll over and play dead because an inspector tells you to.

Re: Aluminum SER? OK or Not #49644
03/12/05 10:59 AM
03/12/05 10:59 AM
H
highvoltageguy  Offline
Member
Joined: Mar 2005
Posts: 53
Silt, Colorado, USA
Electricmanscott quote:
--------------------------------------------------------------------------------
Can the MAN make it rain and snow too?
--------------------------------------------------------------------------------
the issue is not rain and snow.
but if SER ALUM. is ok and what the inspector told him. here in Colorado the inspectors are state inspectors, and whinning and crying with the inspector only going to cause yourself grief, and if the inspector's telling everyone the same thing then everyone's in the same boat.
and like Redogs wrote and looked myself there is no mention of not being able to use alum.,, BUT you will also find that if the local authority (jurisdiction) says otherwise that is what you will have to follow.


[This message has been edited by highvoltageguy (edited 03-12-2005).]

Re: Aluminum SER? OK or Not #49645
03/12/05 11:46 AM
03/12/05 11:46 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
There are leaders and there are followers. While I would not say I am a "Leader" I am absolutely not a follower. Where I work the rules are the rules. The inspectors are bound to follow them as written. Some rules are ambiguous and can be interpreted in different ways, others are black and white. Either way there are no rules that contain the words "Because I said so". So if an inspector makes that claim he can look over his shoulder and he will see I am not following.

Re: Aluminum SER? OK or Not #49646
03/12/05 12:00 PM
03/12/05 12:00 PM
T
tsolanto  Offline OP
Member
Joined: Sep 2002
Posts: 131
Long Island NY
Who exactly is the AHJ the NEC, the State, The town the inspector. Example the New York Board of Fire Underwiters which is an inspection company had a rule that is not in the code. It says no receptacles in closets. Now I think it is a good idea anyway but not in the NEC. you could not get an inspection passed with a receptacle in the closet period. So who is the AHJ in this case it sounds like it is the inspector. I'm confused

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,916
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,510 Are you busy
180,295 Re: Forum
170,799 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.004s) Memory: 1.0233 MB (Peak: 1.1983 MB) Zlib enabled. Server Time: 2018-01-16 11:43:03 UTC