Service feeders ? #49337
03/04/05 07:57 PM
03/04/05 07:57 PM
N
NJ Wireman  Offline OP
Member
Joined: Aug 2004
Posts: 186
New Jersey (South Jersey)
Ok i think i am ready to flip out over this topic, i have had it out with more people over the proper responce to the following?

looking to find out the proper size wires for the below listed services as well as the proper size wire to ground rod and wire to water pipe. I have been arguing this on out way to ften lately so lets see what everyone out goes with. if poss code ref. #'s would be great i go with 310.15(B)(6) myself

Services;
100 amp = wire size cooper & alum.
150 amp= same
200 amp= same

as well as bonding for each.
and ground to ground rods for each.

Work Gear for Electricians and the Trades
Re: Service feeders ? #49338
03/04/05 08:13 PM
03/04/05 08:13 PM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
dwellings??

Re: Service feeders ? #49339
03/04/05 08:32 PM
03/04/05 08:32 PM
N
NJ Wireman  Offline OP
Member
Joined: Aug 2004
Posts: 186
New Jersey (South Jersey)
yes resi. work,
not commercial

Re: Service feeders ? #49340
03/04/05 08:33 PM
03/04/05 08:33 PM
D
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
IF you are sizing for dwelling units, then 310.15(B)(6) is the correct table to determine service conductor sizes.

You say grounding electrode conductors to ground rods - 250.66(A) says #6 copper to the rod regardless of the service size.

Bonding?...bonding what?

Main Bonding Jumper? 250.28(D) says to use Table 250.66 and size your jumper based on the size of the service conductor

Bonding to water pipe (dwelling water service) - 250.66 says to use Table 250.66

Bonding jumper used to connect grounding electrodes together to form the grounding electrode system - 250.53(C) says to size per 250.66

Bonding metal water piping systems installed in or attached to a building - 250.104(A)(1) says to size in accordance with Table 250.66

Re: Service feeders ? #49341
03/04/05 10:03 PM
03/04/05 10:03 PM
N
NJ Wireman  Offline OP
Member
Joined: Aug 2004
Posts: 186
New Jersey (South Jersey)
kicking this back up top again


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,558 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9653 MB (Peak: 1.1018 MB) Zlib enabled. Server Time: 2018-01-20 03:26:25 UTC