Generac Home Stand-by #48480
02/12/05 10:23 PM
02/12/05 10:23 PM
S
sierra electrician  Offline OP
Member
Joined: Feb 2005
Posts: 219
North Fork, CA USA
Has anyone ever installed a remote Start/Stop on these units.
Its a Generac 7kW Air Cooled unit with ATS/Load Center.
HO is old and can't make it to the Gen set to set to the Off position. Her gen ran 7 days straight and sucked her propane tank dry during the last outage.
I am wanting to install a switch at the ATS which is located inside her house. I've poured the schematics and can't determine if this can be done. The only option I can see is tieing into the HOA at the Gen and extending into the house. This is not a job I want to do because of the time it will take to recrawl under the house. This was not a easy feat the first tome around.

Thanks
Rob

Work Gear for Electricians and the Trades
Re: Generac Home Stand-by #48481
02/12/05 10:40 PM
02/12/05 10:40 PM
M
mhulbert  Offline
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
I'm not srue on this specific unit, but most gennies w/ an ats have a simple contact closure to start the engine. So if you tie in at the transfer switch, you should be able to do a HOA switch there.

Maybe the Generac system is different, I've never used on.

Good Luck

Re: Generac Home Stand-by #48482
02/12/05 10:42 PM
02/12/05 10:42 PM
S
sierra electrician  Offline OP
Member
Joined: Feb 2005
Posts: 219
North Fork, CA USA
Yes, they are different they utilize a 4 wire start loop and it feeds into the PCB on the Gen.

Thanks
Rob

Re: Generac Home Stand-by #48483
02/13/05 08:22 AM
02/13/05 08:22 AM
R
rhiphi  Offline
Member
Joined: Jan 2005
Posts: 40
Groton NY
try calling the tech line and ask them
every time i call them they are very helpful

Re: Generac Home Stand-by #48484
02/13/05 03:24 PM
02/13/05 03:24 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
You cant mess with the factory wiring at all on the generator, transfer, any of it. It will void the warranty. You could extend the 15 and 17 wires and work it, but if there is a problem with say the PCB, you cant claim it on the warranty. It ran for 7 days because there was no power? Is the customer just trying to conserve fuel? Another thing, its going to be very hard to get any more wires in the whip from the trans switch. none of the control wires in there will help you, unless you want to control the coils in the transfer switch. Hope that helped some.
........i may have found something for you, there is a terminal board on the generator with 178and 183, this is a remote start contact. should be able to use that for what you want, without altering the factory wiring. now, you just have to get two more control wires through that flex...

[This message has been edited by trekkie76 (edited 02-13-2005).]

[This message has been edited by trekkie76 (edited 02-13-2005).]

Re: Generac Home Stand-by #48485
02/17/05 08:44 PM
02/17/05 08:44 PM
S
sierra electrician  Offline OP
Member
Joined: Feb 2005
Posts: 219
North Fork, CA USA
Trekkie 76
I had found the terminals you metioned on a PDF from Generac. Do these terminals on newer units? There are two different documents one ends with -0 the other ends with -1, I was figuring that one doc is pre 2000 and the other being post 2000.
This gen is about 70mi away so I'm trying to get all the info I need before I return.

Thanks for all your help.
Rob

This board needs a spell check.

Re: Generac Home Stand-by #48486
02/18/05 06:51 AM
02/18/05 06:51 AM
S
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
Last one we did, we did wireless. Installed a series stop switch ahead of the factory stop switch. low voltage xfmr and NC timed relay worked fine. placed the receiver under the housing of the geny for weather protection and the xmitter runs on 9v battery. They push button, NC opens and geny stops. The timed relay stays latched (open in our case) for whatever time we set it for then releases. We set it for 30 seconds to give the xfer switch time to sense the loss of emer power and presence of POCO power and do it's thing. One big thing we had was a xfer setup that, once it lost power to the run loop, would not restart without a start pulse; otherwise it would restart or just sit there with the ignition switch open forever. Wasn't difficult to do and the best part is that nobody can figure out what we did so we now do the annual service which consists of changing batteries and testing xmitters. Kinda like job security. Yeah I know ... that's tacky.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,264
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,392 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.005s) Memory: 0.9842 MB (Peak: 1.1354 MB) Zlib enabled. Server Time: 2018-01-22 16:27:44 UTC