#48075 - 02/03/05 09:47 AM EGC sizeing  
JCooper  Offline
Member
Joined: Dec 2002
Posts: 228
Kendall Park, NJ USA
Hello all, I have an existing Infared electric heater installed, nameplate amps is 25, OCP 30 amps, fed with #8 THWN in 3/4" flex. I am adding another heater right next to this one and I just wanted to make sure that I can share the #8 EGC I pulled the first time, I will just be adding the two ungrounded conductors to feed the second unit in the same raceway. I looked in 250.122 and for 30 ocp the min EGC is #10, and for 60 amp, which would be the total amps drawn by both units the EGC is still #10 so my #8 should be fine, right? Thanks

Jim


Work Gear for Electricians and the Trades

#48076 - 02/03/05 09:54 AM Re: EGC sizeing  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
The EGC should be sized dependant upon the breaker that it needs to trip. For the 30 amp, #10 is typically fine, however, you increased the size of the ungrounded conductors (for voltage drop?), and therefore the EGC must be increased in proportion, requiring a #8 EGC. It sounds to me like your EGC size will be fine.


Ryan Jackson,
Salt Lake City

#48077 - 02/03/05 10:25 PM Re: EGC sizeing  
JCooper  Offline
Member
Joined: Dec 2002
Posts: 228
Kendall Park, NJ USA
Sorry, I forgot to include that, the run is about 100' so I ran the #8 for VD. I thought the egc was alright, I just wanted to make sure I didn't miss something. Thanks

Jim



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.004s) Memory: 0.7509 MB (Peak: 0.8751 MB) Zlib enabled. Server Time: 2017-05-27 13:40:23 UTC