Raintite EMT fittings #47257
01/12/05 09:47 PM
01/12/05 09:47 PM
L
livetoride  Offline OP
Member
Joined: Jan 2005
Posts: 109
san diego ca usa
When installing the new Raintite connectors in a threaded device do you use the rubber washer? On some lights and boxes the female threads start resessed and you can't get but one or two threads but if you remove the washer you can get a good connection. I was taught if it was threaded it was water tight. What are your thoughts? Rod

Work Gear for Electricians and the Trades
Re: Raintite EMT fittings #47258
01/13/05 11:32 AM
01/13/05 11:32 AM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
I haven't used them yet but I would say that you need the "O" ring. Threaded is not necessarily leak proof and this is especially the case with Bell boxes and connectors. It all depends on whether the full taper of the threads on the fitting or conduit fully engage the threads of the box. That's possible with threaded rigid or IMC conduit but with most fittings the limit is reached when the hex or shoulder contacts the box.

-Hal

Re: Raintite EMT fittings #47259
01/13/05 08:43 PM
01/13/05 08:43 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Welcome to the forums!

THe fitting must be used as per the mfg instructions. There are/were an instruction/installation sheet in the last few boxes of RT EMT fittings we bought. I can't say fore sure, but I believe the O-ring is to be used. The UL listing of RT fittings was revoked a while back, as the 'old style' fittings were not 'RT'.

A gut answer will be "use the O-ring"

John


John
Re: Raintite EMT fittings #47260
01/13/05 09:32 PM
01/13/05 09:32 PM
L
livetoride  Offline OP
Member
Joined: Jan 2005
Posts: 109
san diego ca usa
Danm not what I want to hear but I do see your point. On a horizontal run I am more worried about a tight connection, the threads are short I do not see how water can enter if you have 5 threads but what do I know I have only been at it for 26 yrs. Do we have to put rubber gaskets on ridgid too? I am not talking about the ring on the Emt just the crush washer. If 5 threads is good for explosion proof why is it not good for weather tite?

Re: Raintite EMT fittings #47261
01/13/05 09:59 PM
01/13/05 09:59 PM
N
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Quote
If 5 threads is good for explosion proof why is it not good for weather tite?


Because for explosion proof, all the threads do is provide a long enough path to cool the escaping gases below the ignition point of the surrounding atmosphere. They DO NOT have to completely prevent leakage.

Pipe threads generally aren't leakproof without some kind of sealant. Plumbers need to use teflon tape, pipe dope, etc. to keep threaded pipe joints from leaking.

I would use the O-ring unless the instructions say to omit it.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 15
Popular Topics(Views)
243,566 Are you busy
180,366 Re: Forum
170,844 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9667 MB (Peak: 1.1058 MB) Zlib enabled. Server Time: 2018-01-20 21:03:46 UTC