#47204 - 01/11/05 08:27 PM transfer switch and sub panel  
nov  Offline
Member
Joined: Aug 2004
Posts: 69
New Jersey
I have a 200 amp main breaker panel and I am installing a 200 amp auto transfer switch. The SEU cable comes out of the panel and feeds into the transfer switch first the to the main panel. My question is if the transfer switch is hit first does that make the main panel a sub panel. Basically should I treat the transfer switch the same as a service disconnect. If it is a sub I would have to seperate the grounds and the neutrals and feed the main panel with SER cable.


Work Gear for Electricians and the Trades

#47205 - 01/11/05 08:42 PM Re: transfer switch and sub panel  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Yes the ATS will now be the main and the neutrals and grounds at the old panel will need to be isolated.

Question for you, is this a "Service Rated" transfer switch?

It must be in order to install it as you describe.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#47206 - 01/11/05 08:58 PM Re: transfer switch and sub panel  
nov  Offline
Member
Joined: Aug 2004
Posts: 69
New Jersey
I believe it is service rated it is a generac 200 amp transfer switch model 06435
http://www.guardiangenerators.com/support/guardian_transfer_switch.asp


#47207 - 01/11/05 09:12 PM Re: transfer switch and sub panel  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I am not sure that what you linked to is service rated.

I would expect to see accessible disconnect switches to kill the power, it looks like you need a screw driver to open them.

The page mentions UL 1008 Listed which is just a transfer switch listing not necessarily a "Service Rated" transfer switch.

Before purchasing this switch you want to be sure.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#47208 - 01/11/05 09:19 PM Re: transfer switch and sub panel  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
I don’t believe the transfer switch you are proposing to use is rated for use as service entrance equipment. It does not have provisions for a bonding jumper and doesn’t have a means to disconnect the control conductors going to the generator. If you use this switch you should install a service disconnect before the switch. The other model that Generac has listed on that page (Service Disconnect Transfer Switch) might be listed for service equipment but I’m not sure. The Generac reps I have talked to don’t recommend using that transfer switch since the only way to access the service disconnect is to un-bolt and remove the front cover. Apparently many of the users that have used this switch have had inspectors reject the installation.

Curt


Curt Swartz


Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7669 MB (Peak: 0.9052 MB) Zlib enabled. Server Time: 2017-04-23 07:55:42 UTC