Single phase meter on 3-phase system? #46946
01/06/05 10:28 AM
01/06/05 10:28 AM
N
NJwirenut  Offline OP
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Will a standard single phase mechanical watthour meter work properly when used on 2 phases of a 208Y/120 system?

I am installing a bunch of instrumentation, a cabinet air conditioner, and some lighting in a shed located about 300' away from a building. The feeder run to the shed from the building is 2 phases, neutral, and ground of a 3 phase 208V system in the main building. The site owner wants a watthour meter on the side of the shed, so the instrument owner can be billed for the power consumed. Will a standard mechanical watthour meter read properly if the phase difference between the legs is 120 degrees rather than 180, or do i need the more expensive electronic CT type metering here?

Work Gear for Electricians and the Trades
Re: Single phase meter on 3-phase system? #46947
01/06/05 12:22 PM
01/06/05 12:22 PM
A
ameterguy  Offline
Member
Joined: May 2002
Posts: 30
Mass
The short answer to your first question is "no". The single phase meter will meter the 208v loads accurately, but not the 120 volt loads accurately. The 120 volt loads will meter approx 75%, but it will vary up or down based upon the power factor.

For a 200 amp or less service, the meter you should use for this is a 5 jaw "network" meter.

The cost difference between the meters is approx $90.00 (single phase -$30 vs network meter - $120).

I hope this helps

[This message has been edited by ameterguy (edited 01-06-2005).]

Re: Single phase meter on 3-phase system? #46948
01/06/05 02:28 PM
01/06/05 02:28 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
I agree with ameterguy. Ideally, a network meter is used for the described service, but there is a possibly less costly option that is also intended for the application.

Look at www.hialeahmeter.com/self.htm for a (remanufactured/tested) 120V form-12 class-100 or -200 meter. A 5-jaw socket is needed.

Another source is Austin International at www.electricalconnector.com/Remanufactured%20Meters%20Brochure.pdf

Re: Single phase meter on 3-phase system? #46949
01/06/05 03:52 PM
01/06/05 03:52 PM
N
NJwirenut  Offline OP
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Thanks for the info! Ordering a 5 lug meter from Hialeah...

All the loads here will be 120V. One phase for lighting and A/C, the other one for the electronics.

Re: Single phase meter on 3-phase system? #46950
01/07/05 09:51 PM
01/07/05 09:51 PM
C
Clydesdale  Offline
Member
Joined: Nov 2004
Posts: 138
Is it mandatory to isolate the electronics on its own phase?

Re: Single phase meter on 3-phase system? #46951
01/07/05 10:55 PM
01/07/05 10:55 PM
N
NJwirenut  Offline OP
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
I figured that it would help to protect the instrumentation from possible spikes caused by the A/C compressor cycling on and off. There will be a UPS unit backing some of the more critical gear up, as well.

All the electronics are inside a NEMA 12 rack enclosure, with an air conditioner hung on the side of it to maintain the internal temperature. The equipment will be running 24/7/365 for at least the next few years.

Re: Single phase meter on 3-phase system? #46952
12/23/05 04:43 AM
12/23/05 04:43 AM
R
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 856
Titirangi, Akld, New Zealand
Blondells theorem

n-1= meter elements : where n are the phases and neutral, subtract one that tells you how many elements the meter needs.

in your case 2ph + Neutral - 1 = 2 element meter for the correct voltage of the service


The product of rotation, excitation and flux produces electricty.
Re: Single phase meter on 3-phase system? #46953
12/23/05 09:30 AM
12/23/05 09:30 AM
W
WFO  Offline
Member
Joined: Sep 2005
Posts: 202
Cat Spring, TX
Quote:
"The site owner wants a watthour meter on the side of the shed, so the instrument owner can be billed for the power consumed. "

There might be some legallities here that your owner may want to check into. Not sure if this is permitted everywhere.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,576 Are you busy
180,374 Re: Forum
170,850 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.035s Queries: 14 (0.017s) Memory: 0.9919 MB (Peak: 1.1508 MB) Zlib enabled. Server Time: 2018-01-21 10:39:05 UTC