#46946 - 01/06/05 11:28 AM Single phase meter on 3-phase system?  
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Will a standard single phase mechanical watthour meter work properly when used on 2 phases of a 208Y/120 system?

I am installing a bunch of instrumentation, a cabinet air conditioner, and some lighting in a shed located about 300' away from a building. The feeder run to the shed from the building is 2 phases, neutral, and ground of a 3 phase 208V system in the main building. The site owner wants a watthour meter on the side of the shed, so the instrument owner can be billed for the power consumed. Will a standard mechanical watthour meter read properly if the phase difference between the legs is 120 degrees rather than 180, or do i need the more expensive electronic CT type metering here?


Work Gear for Electricians and the Trades

#46947 - 01/06/05 01:22 PM Re: Single phase meter on 3-phase system?  
ameterguy  Offline
Member
Joined: May 2002
Posts: 30
Mass
The short answer to your first question is "no". The single phase meter will meter the 208v loads accurately, but not the 120 volt loads accurately. The 120 volt loads will meter approx 75%, but it will vary up or down based upon the power factor.

For a 200 amp or less service, the meter you should use for this is a 5 jaw "network" meter.

The cost difference between the meters is approx $90.00 (single phase -$30 vs network meter - $120).

I hope this helps

[This message has been edited by ameterguy (edited 01-06-2005).]


#46948 - 01/06/05 03:28 PM Re: Single phase meter on 3-phase system?  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
I agree with ameterguy. Ideally, a network meter is used for the described service, but there is a possibly less costly option that is also intended for the application.

Look at www.hialeahmeter.com/self.htm for a (remanufactured/tested) 120V form-12 class-100 or -200 meter. A 5-jaw socket is needed.

Another source is Austin International at www.electricalconnector.com/Remanufactured%20Meters%20Brochure.pdf


#46949 - 01/06/05 04:52 PM Re: Single phase meter on 3-phase system?  
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Thanks for the info! Ordering a 5 lug meter from Hialeah...

All the loads here will be 120V. One phase for lighting and A/C, the other one for the electronics.


#46950 - 01/07/05 10:51 PM Re: Single phase meter on 3-phase system?  
Clydesdale  Offline
Member
Joined: Nov 2004
Posts: 138
Is it mandatory to isolate the electronics on its own phase?


#46951 - 01/07/05 11:55 PM Re: Single phase meter on 3-phase system?  
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
I figured that it would help to protect the instrumentation from possible spikes caused by the A/C compressor cycling on and off. There will be a UPS unit backing some of the more critical gear up, as well.

All the electronics are inside a NEMA 12 rack enclosure, with an air conditioner hung on the side of it to maintain the internal temperature. The equipment will be running 24/7/365 for at least the next few years.


#46952 - 12/23/05 05:43 AM Re: Single phase meter on 3-phase system?  
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 854
Titirangi, Akld, New Zealand
Blondells theorem

n-1= meter elements : where n are the phases and neutral, subtract one that tells you how many elements the meter needs.

in your case 2ph + Neutral - 1 = 2 element meter for the correct voltage of the service


The product of rotation, excitation and flux produces electricty.

#46953 - 12/23/05 10:30 AM Re: Single phase meter on 3-phase system?  
WFO  Offline
Member
Joined: Sep 2005
Posts: 202
Cat Spring, TX
Quote:
"The site owner wants a watthour meter on the side of the shed, so the instrument owner can be billed for the power consumed. "

There might be some legallities here that your owner may want to check into. Not sure if this is permitted everywhere.



Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7926 MB (Peak: 0.9504 MB) Zlib enabled. Server Time: 2017-04-27 15:00:59 UTC