ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Windows 10, who's upgraded?
by ElectricianBud. 05/27/17 11:02 AM
How do you find a good employee?
by ElectricianBud. 05/27/17 10:58 AM
Recall notice: Bosch Solar panels
by ElectricianBud. 05/27/17 10:53 AM
Correct rotation, wrong sequence
by Potseal. 05/27/17 12:15 AM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,915 Are you busy
171,925 Re: Forum
164,807 Need opinion
Who's Online Now
0 registered members (), 46 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#46345 - 12/19/04 09:36 AM NEC Help  
AndyP  Offline
Member
Joined: Aug 2004
Posts: 20
What is the ampacity of the wire in #11 if it was installed to feed Light poles?

I look in Article 310.16 but I'm just confused.

lol man I'm tired. #11 meaning THHN 8 awg

[This message has been edited by AndyP (edited 12-19-2004).]

[This message has been edited by AndyP (edited 12-19-2004).]


Work Gear for Electricians and the Trades

#46346 - 12/19/04 09:43 AM Re: NEC Help  
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
"What is the ampacity of the wire in #11 if it was installed to feed Light poles?"

Whats #11 refer to?


#46347 - 12/19/04 09:56 AM Re: NEC Help  
AndyP  Offline
Member
Joined: Aug 2004
Posts: 20
Never mind I think it's 55a


#46348 - 12/19/04 10:09 AM Re: NEC Help  
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
Generally conductors below 100amp are rated according to the 60degree column of 310.16.

You must rate the wire to the lowest value of any component in the circuit. The degree rating of the breaker, and any devices, lugs, or equipment, have to be taken into concideration.

8 copper = 40amps for 3 or less conductors.
You have to derate if you have more than three conductors or have ambient temperatures greater than 86 degrees F.

To derate the wire use the 90 degree column if using thhn/thwn.

[This message has been edited by russ m (edited 12-19-2004).]


#46349 - 12/19/04 10:15 AM Re: NEC Help  
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
while you may use the 90 degree column for derating, (use what ever column the wire is rated for) you still have to use the lower of the two values for your conductor ampacity. Meaning the the lower of the two, (1)60 degree column or (2)the derated 90 degree wire.

[This message has been edited by russ m (edited 12-19-2004).]


#46350 - 12/19/04 10:19 AM Re: NEC Help  
AndyP  Offline
Member
Joined: Aug 2004
Posts: 20
Thanks


#46351 - 12/19/04 10:19 AM Re: NEC Help  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Andy it is very unlikely you can use the 90 C column which lists 8 AWG @ 55 amps.

You may very well be able to use the 75 C column if the terminations you are using are rated 75 C. At 75 C 8 AWG CU is rated 50 amps.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#46352 - 12/19/04 10:28 AM Re: NEC Help  
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
It might be helpfull for you to look at article 110.14(C)

I had to edit the article number

[This message has been edited by russ m (edited 12-19-2004).]

[This message has been edited by russ m (edited 12-19-2004).]


#46353 - 12/19/04 12:13 PM Re: NEC Help  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,443
NY, USA



Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,707
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.006s) Memory: 0.7991 MB (Peak: 0.9673 MB) Zlib enabled. Server Time: 2017-05-28 04:42:51 UTC