#44740 - 11/10/04 05:39 PM 3 phase delta  
Kelley  Offline
Member
Joined: Jul 2004
Posts: 28
Masachusetts
I was at a site today (new sewer pump station) that will be supplied from a 3 phase delta. Upon checking the meter socket for power i read 240v to ground on a phase, 0 volts to ground on b phase and 240v to ground on c ph. i get 240 v phase to phase. i dont have much experience on this type of system but i thought b phase was the high leg? i'm a little confused does anyone have an answer as to what i should be reading?

thanks
Kelley


Work Gear for Electricians and the Trades

#44741 - 11/10/04 05:57 PM Re: 3 phase delta  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Your readings are fine.

You have a 3-phase, 3-wire corner grounded delta system, there is no high leg.

A high leg can be found with 3-phase, 4-wire delta systems.

[This message has been edited by iwire (edited 11-10-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#44742 - 11/10/04 06:10 PM Re: 3 phase delta  
Kelley  Offline
Member
Joined: Jul 2004
Posts: 28
Masachusetts
so 240 to ground on a and c phase is ok. thank you iwire

Kelley


#44743 - 11/10/04 08:48 PM Re: 3 phase delta  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
For 240V delta, regardless of system grounding method, be aware that it is a serious misapplication to use less than 250V fuses or other than 240V circuit breakers. 120- or 120/240V-rated circuit breakers are not intended to be used with 3-wire delta electric services. [See UL white book.]


#44744 - 11/10/04 10:02 PM Re: 3 phase delta  
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
Congratulations! You have found the ONE TIME you fuse/switch the "neutral!"


#44745 - 11/10/04 11:40 PM Re: 3 phase delta  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
John,
You can't use a fuse in this grounded conductor unless the fuse is used for motor overload protection. You treat this grounded conductor just like any other white wire.
Don


Don(resqcapt19)

#44746 - 11/12/04 07:39 PM Re: 3 phase delta  
maintenanceguy  Offline
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
By Bjarney:
____
For 240V delta, regardless of system grounding method, be aware that it is a serious misapplication to use less than 250V fuses or other than 240V circuit breakers. 120- or 120/240V-rated circuit breakers are not intended to be used with 3-wire delta electric services. [See UL white book.]
______

Please explain more.


#44747 - 11/12/04 09:58 PM Re: 3 phase delta  
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
resq- You're quite right- the only times I've encountered this type of power, it was used to power well pumps, and the control voltage came off a transformer.

The UL "White Book" says, under "Circuit breakers, moldes case..." that:
"breakers rated 125/250....are suitable for use....where the voltage to ground does not exceed 125v."
I believe that the "White Book" is available at UL's web site.


#44748 - 11/13/04 01:39 AM Re: 3 phase delta  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
also with delta breaker you can not use the slash on the label like 120/240 volts it must be straght 240 volt becaue of line to ground is pretty high btw it will stated in nec but i cant rember where it is excatally located

merci, marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#44749 - 11/13/04 08:35 AM Re: 3 phase delta  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
240.85 Applications. A circuit breaker with a straight voltage rating, such as 240V or 480V, shall be permitted to be applied in a circuit in which the nominal voltage between any two conductors does not exceed the circuit breaker’s voltage rating. A two-pole circuit breaker shall not be used for protecting a 3-phase, corner-grounded delta circuit unless the circuit breaker is marked 1–3 to indicate such suitability.

A circuit breaker with a slash rating, such as 120/240V or 480Y/277V, shall be permitted to be applied in a solidly grounded circuit where the nominal voltage of any conductor to ground does not exceed the lower of the two values of the circuit breaker’s voltage rating and the nominal voltage between any two conductors does not exceed the higher value of the circuit breaker’s voltage rating.

FPN: Proper application of molded case circuit breakers on 3-phase systems, other than solidly grounded wye, particularly on corner grounded delta systems, considers the circuit breakers’ individual pole-interrupting capability.


Charlie Eldridge, Indianapolis Utility Power Guy

Page 1 of 2 1 2

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 