#44478 - 11/05/04 04:33 AM signal reference grid (high-frequency grid) question !  
bucketman  Offline
Member
Joined: Oct 2004
Posts: 72
vancouver WA, USA.
Where in the code book can I find reference to a "high-frequency reference grid system" (or signal-reference grid)? I need to know what kind of grounding point I need to provide in order to prevent unwanted noise.

Thanks!


Work Gear for Electricians and the Trades

#44479 - 11/05/04 09:15 AM Re: signal reference grid (high-frequency grid) question !  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
There is nothing in the NEC regarding this design. Check the IEEE colored book series.


Ron

#44480 - 11/05/04 12:06 PM Re: signal reference grid (high-frequency grid) question !  
dereckbc  Offline
Member
Joined: Oct 2003
Posts: 156
Tulsa, OK
This is a design issue, and not NEC related. There are many good sources for a SRG. Best guidline is in MIL-HNBK-495A and FIPS-94. There are also some guidelines in IEEE Emerald Book, ITU-T K.27, and ANSI T1.333-2001.


#44481 - 11/05/04 12:27 PM Re: signal reference grid (high-frequency grid) question !  
dereckbc  Offline
Member
Joined: Oct 2003
Posts: 156
Tulsa, OK
Bucketman, FWIW, a SRG isn’t bonded to any particular point per se. They can be constructed of either the raised floor grid structure, #6 AWG copper conductor grid under the raised floor, a wire mesh embedded into the concrete or suspended from the ceiling, or a cable rack grid either under a raised floor or suspended from the ceiling. Lots of variables to work with. The important thing is the size of the grid. It depends on the frequency cut-off of interest. The grid is designed on 1/16 of the wavelength, so for a 30 Mhz grid you are looking at something with 2-feet on center. The higher the frequency the smaller the dimensions

As far as bonding or connecting, it is connected to everything like conduits, water pipes, every AC panel EGC bus in the area, all equipment frames, every XO in transformers, every building steel column it passes by, every ground electrode available, etc. The point is not necessarily low impedance to earth, but rather low impedance between any two points on the system and to the power source.

Edited to correct spelling


[This message has been edited by dereckbc (edited 11-05-2004).]


#44482 - 11/06/04 09:28 PM Re: signal reference grid (high-frequency grid) question !  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
A general but obsolete/withdrawn NIST document that introduced a lot of terms and concepts for “signal” versus “power” grounding is www.itl.nist.gov/fipspubs/fip94.pdf Early on, authors Lewis and Kalbach were thought to have landed from Mars with some very revolutionary but much-needed discussion on “convergence” of the two widely conflicting systems, and—equally important—the modes of thinking that fostered the original confusion.



Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7685 MB (Peak: 0.9055 MB) Zlib enabled. Server Time: 2017-09-20 23:47:04 UTC