Underground Long PVC Run #44383
11/02/04 11:49 PM
11/02/04 11:49 PM
I
InspectorE  Offline OP
Member
Joined: Oct 2004
Posts: 51
Hudson WI USA
I have a long run (1300') of PVC for some decorative lighting along a driveway. The lamps will be spaced about 130' apart. I'm wondering what the experience is regarding expansion/contraction of the PVC conduit. I know the temp down at 4' or so is pretty constant, but at 2' I'm not so sure it's constant. I certainly don't want any fittings to pull apart. Above ground, expansion fittings would be mandatory.

Work Gear for Electricians and the Trades
Re: Underground Long PVC Run #44384
11/03/04 12:16 PM
11/03/04 12:16 PM
G
goodwill  Offline
Member
Joined: Aug 2004
Posts: 54
Madison, WI, USA
InspectorE,
300.5(J) ground movement,
and 300.7(B) expansion fittings.
I'm assuming that you are in a zone 3 or 4.(did a google on "frost zones")
I personally probably would not bother with the expansion fittings if you can get down to 48"...like you said, it should stay a constant 55°
anything less than 4', I would put one every 50-100'. 352.44(A) (let's say in the summer the earth is an even 55°, and in the winter it is 32°., so 1.01 inches per 100'.)

Re: Underground Long PVC Run #44385
11/03/04 07:00 PM
11/03/04 07:00 PM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
for conduit that is buried, you will not have to be concerned about expansion fittings.

Pierre


Pierre Belarge
Re: Underground Long PVC Run #44386
11/03/04 10:12 PM
11/03/04 10:12 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,917
Brick, NJ USA
Check Carlon literature, UG is OK without exp. joints. But, you must be stubbing 'up' at the fixture locations, No??

You may get ground heaving conditions by/at the stubs.

BTW, if you have concern, I do not know of any prohibition (NEC) or mfg that says you cannot install exp joints if you want.

John


John
Re: Underground Long PVC Run #44387
11/03/04 11:07 PM
11/03/04 11:07 PM
I
InspectorE  Offline OP
Member
Joined: Oct 2004
Posts: 51
Hudson WI USA
There will be lantern posts (5' high or so?) every 130'. Since it is underground, it has to be wet rated wire, so I'm not too concerned about any leakage/condensation inside the conduit. Stubs will have to be brought up to the posts, that's correct. Fortunately, the lamps are only 25 w or so, the voltage drop won't be a big factor.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,548 Are you busy
180,358 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9663 MB (Peak: 1.1063 MB) Zlib enabled. Server Time: 2018-01-19 17:41:15 UTC