ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
What do you do?
by ghost307. 09/22/17 08:26 AM
Another generator question
by gfretwell. 09/21/17 02:41 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
Linear Power Supply Quits Under Load
by JoeTestingEngr. 09/15/17 11:37 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,870 Are you busy
176,624 Re: Forum
168,536 Need opinion
Who's Online Now
1 registered members (geoff in UK), 57 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#42962 - 09/29/04 08:12 PM Garage Problem  
CRM  Offline
Member
Joined: Feb 2004
Posts: 74
Alberta Canada
Customer has a detached garage, two circuits are run underground in 10/3 underground cable. Two pole 15 amp breaker in house trips maybe once a day for no apparent reason, I checked connections on both ends, replaced breaker, but it still trips, there is no load on when breaker trips. I,m thinking the underground cable might be damaged, but I don't know. I don't have time waiting around the house waiting for it to trip. How would you guys troubleshoot this problem, thanks for any replies.


Work Gear for Electricians and the Trades

#42963 - 09/29/04 08:25 PM Re: Garage Problem  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
I had the same problem sometime ago. Finally i came to the conclusion that it would be the UF cable feeding the BBQ section. So, I hooked up a FLUK 88 meter in series with the circuit and put the setting on the MIN/MAX/AVE setting. Then about evry 5-10 minutes the meter would register 150A,225A or some very high amps like that.(cant remember the exact number but it was very high without any load connected) Any way, I disconnected the UF cable and waited for another 10 Minutes nothing tripped. Reconnected the UF cable after 2 minutes it tripped. So the problem was from the cable somewhere.


Good Luck
Edward

[This message has been edited by Edward (edited 09-29-2004).]


Thanks
Edward

#42964 - 09/29/04 09:08 PM Re: Garage Problem  
twh  Offline
Member
Joined: Mar 2004
Posts: 918
Regina, Sask.
I would use a megger. Ground faults can show on an ohmmeter, but it's a little unreliable.


#42965 - 09/30/04 01:39 AM Re: Garage Problem  
OreElect  Offline
Member
Joined: Mar 2004
Posts: 98
Salem,Oregon.USA
Sounds like you have a fault.
We usually go out and locate the line and paint it.
We then use a fault locater.Isolate both ends,hook up one end to the fault locater voltage output,Adjustable up to 1700 volts.We have a meter with 2 insulated probes connected to it . we poke into to ground on top of the circuit. and follow the needle until we are right on top of the center signal.Dig down and walla,hole in cable. repair it with a heat shrink connector kit,and your ready to reconnect and energize. Works everytime.



Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.7598 MB (Peak: 0.8928 MB) Zlib enabled. Server Time: 2017-09-22 20:27:55 UTC