#42775 - 09/25/04 08:12 PM Alum/Copper bus Panels  
Fred  Offline
Member
Joined: Apr 2001
Posts: 449
Straughn, IN 47387
I am curious to know what bus material the panels you most frequently install have. Copper, Aluminum or plated Copper? I know that location plays in to this selection sometimes, but if it doesn't, why do you prefer what you prefer?


Work Gear for Electricians and the Trades

#42776 - 09/25/04 08:42 PM Re: Alum/Copper bus Panels  
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Copper, We use the CH Classic Loadcenters, We just use, good quality material on all our jobs, better contact with copper, and the breakers are better quality.
We tried other Loadcenters, and after problems, and expensive call backs we went back to CH.
SQ D is another good Loadcenter, but we can't use it on service upgrades where they are bottom feed, because SQ D has neutral bars all clustered next to Main Breaker, and all the neutral wires would have to be spliced to reach the bars.

[This message has been edited by LK (edited 09-25-2004).]


#42777 - 09/26/04 06:52 AM Re: Alum/Copper bus Panels  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
LK, you could turn the SQ D panel upside down. Also there is no reason you can't splice the neutrals. I usually use Siemens for no special reason other than thats what my main supplier carries. I could not even tell you what the bus is made from.


#42778 - 09/26/04 12:38 PM Re: Alum/Copper bus Panels  
Fred  Offline
Member
Joined: Apr 2001
Posts: 449
Straughn, IN 47387
We only have one supply house in town and they carry Siemens ITE. They have their stock loadcenters in either copper or aluminum bus. If you order tubs with interiors that take bolt-ins they are usually plated copper bus. I started dealing with a supply house in a neighboring town last year that carries GE Powerline Gold Series loadcenters. They come standard with tin plated copper bus, even the stab-in loadcenters. SQD QO loadcenters are all plated copper bus. SQD Homeline are aluminum only. I prefer copper and in situations where the loadcenter is in an unheated area, I prefer the plated copper bus.


#42779 - 09/26/04 06:09 PM Re: Alum/Copper bus Panels  
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Scott,

quote,

_________________________________________
"LK, you could turn the SQ D panel upside down. Also there is no reason you can't splice the neutrals. I usually use Siemens for no special reason other than thats what my main supplier carries. I could not even tell you what the bus is made from."

____________________________________________

When you turn the SQ D upside down, the neutral bars are at the bottom of the panel,
and yes there is a reason we can't splice the neutrals, the inspectors in this area, will accept, one or maby two splices, and that is it, all other splices they want in boxes outside the panel, also you can't get away with running the lines from bottom to top of loadcenter breaker, it will fail for loadcenter not to be used as raceway, we argued this was not in the code and the inspector said you are right, it is in the manufacture instructions, do it right and i will be back.

[This message has been edited by LK (edited 09-26-2004).]


#42780 - 09/26/04 06:53 PM Re: Alum/Copper bus Panels  
Norstarr  Offline
Member
Joined: Sep 2004
Posts: 86
Wi
Say LK, I'm lost on how that inspector is calling the panel a raceway because you ran the conductors from the bottom of the panel to the terminations at the top. Seems to me the same would apply with branch circuits entering at the bottom and running to a top breaker. I would be willing to bet that the manuf meaning is to not allow conductors to run through the panel without terminating. As to limiting the number of splices in a panel, it must be an opinion of the local inspector. Do they have a written ordinance requiring this or does each electrician find out the hard way? Makes for a lot of extra work.


#42781 - 09/26/04 10:22 PM Re: Alum/Copper bus Panels  
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Norstarr,

Yes thst was my understanding of the manufacture, they say gutter and i belive they mean riser feeds, however more then one inspector has knocked this method down, good topic to bring to inspector site.
As for the splicing in the panel, most inspectors in my area will let one or two get by.


#42782 - 09/26/04 11:09 PM Re: Alum/Copper bus Panels  
SolarPowered  Offline
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
FYI, Square D has a "remodel" panel with a built-in splice block for splicing all those pesky wires that end up too short when you replace a panel. I wonder what your inspector whould think about that??


#42783 - 09/27/04 07:09 PM Re: Alum/Copper bus Panels  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
LK I'll count this as another misguided inspector. [Linked Image]


#42784 - 09/27/04 07:17 PM Re: Alum/Copper bus Panels  
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
Solar,

There is a QO Remod Panel?
The Supply house asked if i had any numbers, do you have more info.


Page 1 of 2 1 2

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.234s Queries: 15 (0.217s) Memory: 0.8167 MB (Peak: 0.9924 MB) Zlib enabled. Server Time: 2017-04-29 05:39:35 UTC