Remote Gazebo #41637
09/03/04 10:35 AM
09/03/04 10:35 AM
S
SJT  Offline OP
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
We have a Gazebo (concrete slab approx. 50x20) to wire that will have few lights and receptacles. It will be used for people to have parties, BBQS, etc. To stay code compliant, is it OK to run 2 - 20 amp ckts. out to the structure, or do I have to install a 2ckt. sub-panel at the structure. All sides are open on this patio and the breaker panel that I will run the ckts. from is approx. 50' away. I was going to go with a sub- panel, and another Elec. said I did not need it. Thanks for the input.

Work Gear for Electricians and the Trades
Re: Remote Gazebo #41638
09/03/04 10:51 AM
09/03/04 10:51 AM
A
amp-man  Offline
Member
Joined: Jun 2001
Posts: 141
Sacto, California US of A
If you run a multi-wire circuit (i.e., an Edison ckt--two hots off diff. legs & a neutral), there's no need for a subpanel. And of course you need an equipment grounding conductor. So some 12/3 wg UF will do the trick, or bk, red, wht, grn THHW in pipe.

Cliff

Re: Remote Gazebo #41639
09/03/04 12:07 PM
09/03/04 12:07 PM
S
SJT  Offline OP
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
I plan on running seperate nuetrals. One ckt. for the lights, one for the outlets. When I was going through the code, in the ground section with diffrent buildings, structures, etc., I was getting into the panel idea, but it sounds like it's not required.

Re: Remote Gazebo #41640
09/03/04 01:02 PM
09/03/04 01:02 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I strongly suggest the use of the multiwire branch circuit as amp man suggested, it is better for voltage drop.

Also one multiwire branch circuit will not require a ground rod to be driven at the Gazebo. If you run two - 2 wire circuits you must drive a ground rod and connect it to the EGC at the gazebo. 250.32(A) be sure to read the exception.

You will also need disconnects at the gazebo for the circuits you run out there. 225.31

This could be one double pole switch or two single pole switches.

Good Luck, Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,405 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.9579 MB (Peak: 1.0879 MB) Zlib enabled. Server Time: 2018-01-23 11:58:50 UTC