Smart Box Mirrored? #41563
08/30/04 09:17 PM
08/30/04 09:17 PM
S
SolarPowered  Offline OP
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
I'm trying to figure out if I'm going senile... Didn't the Smart Box ads on this site have the screws pointing to the left until the last day or two?

Work Gear for Electricians and the Trades
Re: Smart Box Mirrored? #41564
08/30/04 09:43 PM
08/30/04 09:43 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
[Linked Image]

I changed the picture, but it was probably 2 weeks ago.

[Linked Image]
Bill

Re: Smart Box Mirrored? #41565
08/30/04 09:53 PM
08/30/04 09:53 PM
E
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
I've got a question about these boxes. What's the purpose? We've been taking standard boxes and screwing them to the stud with sheetrock screws as long as I've been in the trade. Why would you need this box?

Re: Smart Box Mirrored? #41566
08/30/04 10:05 PM
08/30/04 10:05 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I E-mailed the manufacturer and asked how compliance with 314.23(B)(1) could be achieved. They haven't responded.


BTW: I don't have my book here, so sorry if the reference is off a little. I'm thinking of the section that says "nails and screws".


Ryan Jackson,
Salt Lake City
Re: Smart Box Mirrored? #41567
08/30/04 10:16 PM
08/30/04 10:16 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Now isn't the screw an ungrounded conductive material to outside the box??????

A violation? 314.43?

Quote
Provisions for supports or other mounting means for nonmetallic boxes shall be outside of the box, or the box shall be constructed so as to prevent contact between the conductors in the box and the supporting screws.


Been wondering....

[This message has been edited by e57 (edited 08-30-2004).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Smart Box Mirrored? #41568
08/30/04 11:48 PM
08/30/04 11:48 PM
S
SolarPowered  Offline OP
Member
Joined: Jul 2004
Posts: 625
Palo Alto, CA, USA
Quote
I changed the picture, but it was probably 2 weeks ago.

Thanks! Glad to know I haven't completely lost it, yet. [Linked Image]

Re: Smart Box Mirrored? #41569
08/31/04 12:12 AM
08/31/04 12:12 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Quote
I E-mailed the manufacturer and asked how compliance with 314.23(B)(1) could be achieved
Ryan,

I'm guessing this is an instance where Code language hasn't caught up with all the new products.
Quote
Provisions for supports or other mounting means for nonmetallic boxes shall be outside of the box, or the box shall be constructed so as to prevent contact between the conductors in the box and the supporting screws.
e57,

The screws are countersunk even below flush, so I don't see then contacting or causing damage to any conductors.

Bill

Re: Smart Box Mirrored? #41570
08/31/04 01:45 AM
08/31/04 01:45 AM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
So whats the deal in changing it... Lefty, or just trying to see if SolarPowered would notice?

Bill from the pic I caould tell if they were countersunk or not, but been wondering about that for a while/

Anyway, I have been a fan of this box... Don't use nail ons anymore, do whole houses in them... I have using them for a simular purpose as the Smart box there. (Haven't seen them anywhere yet... Except this site.)

www.carlon.com/Brochures/2B1-Adjustable.pdf

As a cut-in. Take the box off. A quick modification with snips or a band saw, to cut off the front part of its mounting bracket, and a few holes too. Then put the bracket in the wall, and box back on the bracket. I think they should make them that way, with break off tabs. etc.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Smart Box Mirrored? #41571
09/01/04 05:58 PM
09/01/04 05:58 PM
T
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
We use those adjustable boxes too. LOVE em! never tried to use them as a cut-in, though. cuold work I guess. How do you screww to 2 screws in the front of the bracket ?

[This message has been edited by trekkie76 (edited 09-01-2004).]

Re: Smart Box Mirrored? #41572
09/01/04 06:43 PM
09/01/04 06:43 PM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
trekkie76,

Find your stud, and cut the hole so the side lines up. Then remove the box from the bracket. Then cut off most of the front of the bracket with snips or a saw, (band saw worrks best)leave a 1/4" of the front part. Then drill 2 holes at the corner of the bracket where it fold from the front to the side. (Easiest to do this from the back.) Then line it up in the hole, and smack that 1/4" of whats left of the front part between the rock or plaster and the stud. Put your 2 screws in the holes you made. (the ones in the side if you can reach at the angle too. ) Put the wire in the box, and box back on the bracket. Trim...

It seems like a lot to do, but once you've done it once, it's easy!

Someones gonna say, "Why don't you just use a cut in box." On some of the plaster and lath walls here there's almost a 1/2" between the lath. Or weak sheetrock. First time you plug something in, the box gets pushed though the brittle plaster or rock, or worse the box comes right out of the wall! So check the the first hole, and if the plasters is bad and crumbly, I cut the rest at the stud, and do the above. So I have a nice solid box!

Also, like mentioned above it's a code violation to put screws into a NM box not made to have them. 314.43 Or, 314.23B1 as Ryan mentioned.

These Smart Box things would probhably work well for the same, but like I said, I haven't seen them anywhere yet.

Does anyone know if they are plastic, or bakelite? If the later, I won't touch 'em. Oh, how I hate bakelite...........


Mark Heller
"Well - I oughta....." -Jackie Gleason
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,576 Are you busy
180,374 Re: Forum
170,852 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.005s) Memory: 1.0252 MB (Peak: 1.2012 MB) Zlib enabled. Server Time: 2018-01-21 12:44:48 UTC