ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Dimmable LED 2x4 lay in fixtures
by Potseal. 04/23/17 07:18 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
Electrode boilers question
by SteveFehr. 04/21/17 08:32 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,646 Are you busy
169,329 Re: Forum
162,664 Need opinion
Who's Online Now
0 registered members (), 40 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#41509 - 08/29/04 02:56 PM 700A Main Breaker nuisance tripping  
mgd001  Offline
Junior Member
Joined: Aug 2004
Posts: 2
Santa Rita, GU usa
Hi, this is my first post, happy to be on this forum.

The main breaker for our 3-phase/460v building power tripped on Friday and the Emergency Generator and ATS switched on. I noticed that the Genset out put display showed this: 468 v ,60hz , 715 amps total.

but each seperate phase measured around 235amps. is this enough to trip the breaker due to overloading?

I thought that a breaker marked 700 amps could hold 700 amps per pole?

thanks to all.


Work Gear for Electricians and the Trades

#41510 - 08/29/04 03:39 PM Re: 700A Main Breaker nuisance tripping  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I am a little confused with how many amps you are drawing, I have never seen a generator with a "Total Amps" meter.

If you have 235 amps per phase then we would say the breaker has a 235 amp load.

Each pole of a 700 amp breaker is rated 700 amps but we do not call it a 2100 amp breaker.

A typical 700 amp breaker should not be loaded to more than 80% (560 amps per leg) for periods exceeding 3 hours. That is unless you have a 100% rated breaker, most are not.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#41511 - 08/29/04 05:10 PM Re: 700A Main Breaker nuisance tripping  
mgd001  Offline
Junior Member
Joined: Aug 2004
Posts: 2
Santa Rita, GU usa
The amps draw per leg was around 235 each. a=235amps, b=235amps, c=235amps

Thanks for the clarification.

Our Generator was installed a few weeks ago and it has a slick microprocessor display, with the Total amps reading.

This 700 amp breaker has a little switch assembly Called a "ground-censor" on the panel below the breaker that could be sensing a fault somewhere.

I'll post more details soon.



Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7502 MB (Peak: 0.8757 MB) Zlib enabled. Server Time: 2017-04-24 09:13:54 UTC