Possible alternate path to ground? #40699
08/01/04 01:28 PM
08/01/04 01:28 PM
E
e57  Offline OP
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Looking at a sub-panel installation the otherday, that had a uni-strut frame for support, bolted to a concrete garage floor.

The panel is grounded to the main properly, but would the metal frame be considered an unintentinal alternate path to ground?

Any comments on this?

Having seen a short clear on equipment bolted to a floor once, through the bolt, made me think of this. (Not properly grounded)


Mark Heller
"Well - I oughta....." -Jackie Gleason
Work Gear for Electricians and the Trades
Re: Possible alternate path to ground? #40700
08/01/04 03:02 PM
08/01/04 03:02 PM
W
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
Isn't the case of the sub panel grounded with a ground bar?

Re: Possible alternate path to ground? #40701
08/01/04 06:48 PM
08/01/04 06:48 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
Or rather isn't the panel supplied with an EGC through either the metallic raceway or a separate equipment grounding conductor as a sub panel should be? If that's the case what difference would it make if there were additional ground paths? Could only help.

-Hal

Re: Possible alternate path to ground? #40702
08/01/04 09:11 PM
08/01/04 09:11 PM
D
dereckbc  Offline
Member
Joined: Oct 2003
Posts: 156
Tulsa, OK
“The panel is grounded to the main properly, but would the metal frame be considered an unintentional alternate path to ground?”

Absolutely, that is why the NEC requires an EGC, or a planned path of sufficiently low impedance and capacity to operate an OCPD quickly and safely. There are several names for this path depending on what industry you are in such as local grounds, incidental grounds, foreign ground, ground loops, etc. In my industry, telephony, we call it the “integrated ground plane”.

For the most part it is harmless, but not allways. It is a fact of life in almost any industrial application where you have panels, raceways, and equipment fastened to structural steel, concrete, and rebar within the facility. Most of the problems associated with these unplanned paths are allowing noise currents on the ground circuits, and allowing fault and lightning currents to flow through equipment frames.

In the telephony industry, on certain types of data, transmission, and switching equipment, we single point ground the power source like a DC plant or isolation transformer, and completely isolate all the raceways, distribution equipment, and equipment frames from the “integrated ground plane” to form what we call the “isolated ground plane”. This “isolated ground plane” prevents any noise, fault, or lightning currents from entering via the single point ground method. Similar to the isolated ground receptacles, except it takes more planning, expense, installation techniques, and care to accomplish.


[This message has been edited by dereckbc (edited 08-01-2004).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 13
Popular Topics(Views)
243,605 Are you busy
180,418 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.9589 MB (Peak: 1.0904 MB) Zlib enabled. Server Time: 2018-01-24 03:49:48 UTC