#40002 - 07/10/04 01:17 PM fire alarm relay for elevator  
estman  Offline
Junior Member
Joined: Jul 2004
Posts: 3
hello everyone,

I am putting together a fire alarm system.
The panel is an edwards 2414 which is a basic analog one. my question is how I Interface it with the elevator for a recall?
Thanks,
estman


Work Gear for Electricians and the Trades

#40003 - 07/10/04 01:34 PM Re: fire alarm relay for elevator  
CRM  Offline
Member
Joined: Feb 2004
Posts: 74
Alberta Canada
The fire alarm panel will have a combination NO/NC alarm contacts. I would use the NO contacts and connect these back to the elevator control panel. The elevator company will show you where to wire into their panel. So when there is an alarm a set of contacts will close, operating the elevator recall at the elevator control panel.


#40004 - 07/10/04 03:51 PM Re: fire alarm relay for elevator  
Anonymous
Unregistered

Here's another idea.
I would not recall the elevator on general alarm. I would use a relay type base for the smokes in the elevator lobbies. Wire the relays in parallel so that a fire in any lobby but the main entrance lobby sends the car to first floor (primary) and a fire in the main entrance lobby will send the car to a different floor. (alternate) Also if your shunting the power to the elevator machine room with a heat detector just use a two pole heat using one side for fire alarm and the other side for shunt. Is the building sprinked? It will make a difference on the detection you put in the shaft. You may want to read through NFPA 72 3-9.3 (1999) and a call to the elevator inspector might be worth it. Since, in my area anyway each inspector seems to want it set up a little differently.


#40005 - 07/14/04 03:09 AM Re: fire alarm relay for elevator  
estman  Offline
Junior Member
Joined: Jul 2004
Posts: 3
thank you guys your answers shed light in my questions.



Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31