ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Dimmable LED 2x4 lay in fixtures
by Potseal. 04/23/17 07:18 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
Electrode boilers question
by SteveFehr. 04/21/17 08:32 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,646 Are you busy
169,329 Re: Forum
162,664 Need opinion
Who's Online Now
0 registered members (), 40 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#39879 - 07/05/04 08:31 PM storable swimming pools  
acetoday  Offline
Member
Joined: Sep 2003
Posts: 35
Manassas, Va
I have an above ground swimming pool located approx 200 ft from the panel. Is it permissable to install UF cable 12 inches deep directly to the line side of a GFCI receptacle and then the load side to the pump (single receptacle 6ft from inside wall of pool).

In reviewing the code I haven't seen anything that disallows UF cable for a storable pool pumps. Any help would be appreciated.....


Work Gear for Electricians and the Trades

#39880 - 07/05/04 08:39 PM Re: storable swimming pools  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Look at 680.30 and 680.20(A)(1).
Don


Don(resqcapt19)

#39881 - 07/05/04 08:50 PM Re: storable swimming pools  
acetoday  Offline
Member
Joined: Sep 2003
Posts: 35
Manassas, Va
Don,

Thanks for the info, but I've already reviewed these sections and they did not address my question regarding UF cable.

By the way, 680-20 (a) (1) Pertains to Permanently Installed Pools and not Storable Pools.


#39882 - 07/06/04 12:34 AM Re: storable swimming pools  
sparkystudent  Offline
Member
Joined: Apr 2004
Posts: 42
Staples, MN. USA
to address the issue of depth look to table 300.5 (02 nec) minimum cover requirements look at column 4 and and all locations not specified below would allow for 12 in burial depth...but must put the GFCI protection and 20 amp ocpd in the panel or in the house(ie breaker or gfi and load out to the pool).


#39883 - 07/06/04 08:05 AM Re: storable swimming pools  
acetoday  Offline
Member
Joined: Sep 2003
Posts: 35
Manassas, Va
Sparky,

Thank you for your reply. So far it looks like I'm within code although the real question is the use of UF cable. An Inspector failed this install due to the use of UF cable. I would nornally have installed this with PVC However, the homeowner was trying to save some money (he dug the trench as well). In the mean time his yard is all a mess. Still trying to get resolution.

Thanks again,
Bob


#39884 - 07/06/04 06:12 PM Re: storable swimming pools  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
So long as you don't have an underwater luminaire in this storable pool, the use of UF to serve a remote receptacle in the yard for the double insulated pump is allowed.
680.6 allows the pool receptacle (within 10-20 feet)to be fed with UF.
If you do have a luminaire, then the requirements of 680.23 kick in, and an insulated ground is required; 680.33


Earl

#39885 - 07/06/04 08:13 PM Re: storable swimming pools  
acetoday  Offline
Member
Joined: Sep 2003
Posts: 35
Manassas, Va
Thanks again to all who have responded!

Here is what the inspector stated today. The reason he failed the inspection was due to 680-25.(c) which pertain to motors. In a nutshell it states that the equipment grounding conductor shall be insulated and installed with the circuit conductors in ...rigid nonmetallic conduit etc...).

In reading this section it does seem that PVC is required. I also verified this in the Stallcup's Electrical Design Book which stated the grounding conductor must be installed and run with the circuit conductors in rigid metal conduit, intermediate metal conduit, or rigid nonmetallic conduit from the panelboard to the deck.

Looks like a costly lesson for me.


#39886 - 07/06/04 10:30 PM Re: storable swimming pools  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
If what you have is in fact a "Storable Pool" 680.25 C does not apply. All you need is a gfci receptacle. No bonding either. I see no reason you could not use UF cable for this receptacle as long as the wiring is not within 5' of the pool. Even if there is a luminaire I don't see a requirement for an insulated equipment ground on a storable pool.


#39887 - 07/06/04 11:43 PM Re: storable swimming pools  
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
680.30 says" Storable pools shall comply with sections I & III. 680.25 is in section II.


Choose your customers, don't let them choose you.

#39888 - 07/07/04 08:01 AM Re: storable swimming pools  
acetoday  Offline
Member
Joined: Sep 2003
Posts: 35
Manassas, Va
Obsaleet/Electricmanscott,

I hope you are both right however, 680-30 does not state "shall comply with Sections I and II.

Am I missing something? What confuses me is 680-25 (c) does state specific grounding requirements (i.e., insulated grounding conductor) for pool associated motors but does it really apply to storable pools, by the way there are no lighting fixtures for this above ground pool.

I really appreciate your helping out with this issue.

Bob


Page 1 of 2 1 2

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.8149 MB (Peak: 0.9914 MB) Zlib enabled. Server Time: 2017-04-24 09:19:45 UTC