#39739 - 06/28/04 10:31 PM Conductors in Parallel  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I have seen 800 amp services using two 500 kcmil conductors for each phase. I'm assuming that the ampacity is figured as 430 amps(THHN) X 2 = 860 amps, rather than as being equivalent to one 1000 kcmil conductor at 615 amps. Would three 250 kcmil parallel conductors be 290 amps X 3 = 870 amps?

Dave


Work Gear for Electricians and the Trades

#39740 - 06/28/04 10:53 PM Re: Conductors in Parallel  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
The ampacity is figured using the 75 deg table (380A). Times two conductors is 760A. Then article 240.4 is applied allowing the next higher standard fuse size or 800A.


#39741 - 06/29/04 09:33 AM Re: Conductors in Parallel  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The 75 degree section is used because of the rating of the termination lugs. See 110.14(C).

Remember also to apply 310.15(B)(2)(a) and derate the conductors if you pull all of the paralled conductors in one conduit.

Earl


Earl

#39742 - 06/29/04 12:04 PM Re: Conductors in Parallel  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
The 75C column must be used because UL does not list Overcurrent Protective Devices for use with conductors based on 90C ampacities.


#39743 - 06/29/04 05:24 PM Re: Conductors in Parallel  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
One little detail to watch out for is to be sure that the noncontinuous load plus 125% of the continuous load does not exceed 760 amps for parallel 500kcmil. This is usually not the case since most of us don't cut these things real close to the bone & leave some room for future growth.

Tom


Few things are harder to put up with than the annoyance of a good example.


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7672 MB (Peak: 0.9046 MB) Zlib enabled. Server Time: 2017-07-23 16:52:44 UTC