06/28/04 06:45 PM
06/28/04 06:45 PM
C
ccdave  Offline OP
Member
Joined: Jan 2003
Posts: 59
culver city,calif. usa
Anyone please!
where do I find the requirment for alerts/alarms for doors leading to a pool area for SFD's. What is the minimum db?
dave

Work Gear for Electricians and the Trades
Re: pool alert #39667
06/28/04 07:00 PM
06/28/04 07:00 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
It would most likely be in your local building code. It's not an NEC issue. Call the local building Dept.

Re: pool alert #39668
06/29/04 08:39 AM
06/29/04 08:39 AM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
This is what the 2003 IRC has to say:


Where a wall of a dwelling serves as part of the barrier one of the following conditions shall be met:
9.1. The pool shall be equipped with a powered safety cover in compliance with ASTM F1346; or
9.2. All doors with direct access to the pool through that wall shall be equipped with an alarm which produces an audible warning when the door and its screen, if present, are opened. The alarm shall sound continuously for a minimum of 30 seconds immediately after the door is opened and be capable of being heard throughout the house during normal household activities. The alarm shall automatically reset under all conditions. The alarm system shall be equipped with a manual means, such as touchpad or switch, to temporarily deactivate the alarm for a single opening. Such deactivation shall last for not more than 15 seconds. The deactivation switch(es) shall be located at least 54 inches (1372 mm) above the threshold of the door; or
9.3. Other means of protection, such as self–closing doors with self–latching devices, which are approved by the governing body, shall be acceptable so long as the degree of protection afforded is not less than the protection afforded by Item 9.1 or 9.2 described above.

Hope this helps

Earl


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 12
Popular Topics(Views)
243,606 Are you busy
180,418 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9493 MB (Peak: 1.0741 MB) Zlib enabled. Server Time: 2018-01-24 05:47:52 UTC