#39542 - 06/24/04 06:49 PM grounding two meter service  
richard  Offline
Member
Joined: Aug 2003
Posts: 95
L.I. New York
I installed a two meter service, one feeds a two pole 40, and the other was an upgrade from 100 to 150. I ran a #4 to the water main and used it for the 150 panel. I reused the #6 for the 40 amp panel. I installed two ground rods, one for each panel, seperate from each other. The boss said I was supposed to bond all the grounds together, by running just the #4 from the 150 to the water main, and bug a #6 from the 40 to it, as well as running both ground rod wires to one ground rod. Is there a code that is specific to this situation. (I live on Long Island, Suffolk County, New York. I don't see anything in LIPA"S redbook.


Work Gear for Electricians and the Trades

#39543 - 06/24/04 07:07 PM Re: grounding two meter service  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
in 250-50, if available on the premises, each item 1-6, shall be bonded together to form the grounding electrode system.
1. metal underground water pipe
2.metal frame of a building
3.concrete encased electrode
4.ground ring
5.rod or made electrode
6.plate electrodes


#39544 - 06/25/04 07:20 AM Re: grounding two meter service  
velect  Offline
Member
Joined: May 2004
Posts: 81
st joseph mi usa
I did a similar service

I ran #6 from one panel to the other and then out to two ground rods 6 foot apart. One continuous ground going right through one of the neutral bar lug and through both clamps on the groumd rods. Then took a #4 bond wire and bonded the water and gas system out of one of the panels.

Passed with no problems


#39545 - 06/25/04 02:55 PM Re: grounding two meter service  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
What size is the service conductors that feed the 2 gang meter (double meter). You base the size of the ground wire back to the water pipe on 250.66. From that, I would bug off to each panel, and not jump from one Bus to the other.


#39546 - 06/25/04 07:34 PM Re: grounding two meter service  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,457
NY, USA
Quote
I guess I didn't look hard enough in the redbook.

- richard
[Linked Image]



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.034s Queries: 14 (0.019s) Memory: 0.7683 MB (Peak: 0.9077 MB) Zlib enabled. Server Time: 2017-09-22 15:25:06 UTC