insulated and isolated. #39479
06/21/04 03:59 PM
06/21/04 03:59 PM
S
Sandro  Offline OP
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Please explain the difference between an insulated and an isolated ground line. Are they not one and the same?

Work Gear for Electricians and the Trades
Re: insulated and isolated. #39480
06/21/04 04:10 PM
06/21/04 04:10 PM
N
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
An insulated ground is just that, an insulated (green) ground wire.

An isolated ground wire is a ground wire that runs all the way back to the service ground, without being connected to raceways or boxes along the way. Occasionally used with sensitive electronic equipment to provide a "clean ground" in electrically noisy environments.

Re: insulated and isolated. #39481
06/21/04 08:41 PM
06/21/04 08:41 PM
S
Sandro  Offline OP
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
The code requires an insulated ground in each receptacle found in a patient care area. If I connect this to a dedicated ground from the panel, then its basically an isolated ground is it not? I don't see the wisdom in simply tying off the insulated ground from the receptacle to the nearest j-box ground. What would be the point of having an insulated ground then?

Re: insulated and isolated. #39482
06/21/04 10:08 PM
06/21/04 10:08 PM
Radar  Offline
Member
Joined: Apr 2004
Posts: 349
Los Angeles, CA
Actually, it is not. When you install an isolated ground conductor and utilize an IG receptacle, the ground prong does not connect to the metalic strap of the receptacle. So, when using an IG receptacle, you need 2 grounds: an insulated green equipment grounding conductor to connect the raceway / outlet box / metalic strap of the receptacle, and a separate isolated ground conductor connected only to the receptacle's ground connector (and run back to the main as NJWirenut said).

The idea is to separate the receptacle's ground connection from the 'dirty' equipment ground.

Hope that helps some.
Radar


There are 10 types of people. Those who know binary, and those who don't.
Re: insulated and isolated. #39483
06/22/04 07:28 AM
06/22/04 07:28 AM
C
CDN_ELECTRICIAN  Offline
Member
Joined: Jan 2003
Posts: 73
Concord,Ontario,Canada
Sandro

Section 24 of your code book covers this.
If you go to "Appendix B" and look up the rule number,it explains the intent of the rule.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,560 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.9658 MB (Peak: 1.1055 MB) Zlib enabled. Server Time: 2018-01-20 07:22:53 UTC