ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
jraef 4
Recent Posts
Dryer, Range grounding from "Main" panel
by gfretwell. 05/24/17 09:35 PM
210.70 / Wall Switch / When adopted?
by gfretwell. 05/24/17 09:18 PM
Any UL 508 experts out there?
by sparkyinak. 05/23/17 11:04 PM
Heat pump conundrum
by sparkyinak. 05/21/17 08:49 PM
Interesting week
by HotLine1. 05/20/17 11:57 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,738 Are you busy
171,748 Re: Forum
164,689 Need opinion
Who's Online Now
0 registered members (), 51 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#39090 - 06/08/04 10:11 PM Isolated ground runs.  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Do I need to run a separate ground from the panel to EACH isolated ground receptacle, or can I run a single insulated ground conductor from the panel and stop off at each junction box and pick up each IGR at each station JB? Is there a limit to how many IG I can pick off of a single line?


Work Gear for Electricians and the Trades

#39091 - 06/08/04 11:14 PM Re: Isolated ground runs.  
twh  Offline
Member
Joined: Mar 2004
Posts: 915
Regina, Sask.
In Canada, see rule 10-906(9)


#39092 - 06/09/04 03:26 AM Re: Isolated ground runs.  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
It is up to you and the job specifications.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#39093 - 06/09/04 05:10 PM Re: Isolated ground runs.  
Radar  Offline
Member
Joined: Apr 2004
Posts: 349
Los Angeles, CA
IG doesn't mean dedicated ground for each outlet. As Iwire says, check your specifications. Generally it means a separate isolated and insulated grounding wire besides the equipment grounding conductor.

So, for a 120V outlet, one would end up with a hot, a neutral, an equipment ground (for the conduit & outlet box), and an isolated ground (for the ground prong of a receptacle).

You can usually string several IG outlets together without a problem, depending on specifications. However, some engineers and/or specifiers have different ideas about what IG means.

Lastly, if the breaker panel feeding your circuit does not have an IG bus with an upstream isolated ground conductor back to the main, are you really getting an isloated ground?

Radar


There are 10 types of people. Those who know binary, and those who don't.


Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7601 MB (Peak: 0.8904 MB) Zlib enabled. Server Time: 2017-05-25 06:46:55 UTC