Generators #38969
06/07/04 06:32 AM
06/07/04 06:32 AM
C
cephus  Offline OP
Junior Member
Joined: Jun 2004
Posts: 2
Pikeville, ky, us
During our recent power outage, some of my neighbors had a problem with generators. One owns a gas station and he mentioned that everytime he connects the generators to his gas pumps it destroys the electronic circuit boards of the pumps. I thought that maybe the voltage regulator is not working right in the generator. Has anyone had this problem and if so, what can we do?

Work Gear for Electricians and the Trades
Re: Generators #38970
06/07/04 07:27 AM
06/07/04 07:27 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Many smaller generators do not have an automatic voltage regulator.


Ron
Re: Generators #38971
06/07/04 07:37 AM
06/07/04 07:37 AM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
It is often not merely a voltage regulator problem. You need to pay attention to "Total Harmonic Distortion" (THD) and try for the lowest # you can find ( go for under 5%) or the variance will react badly on semi-conductors, sometimes they will not work at all.

Re: Generators #38972
06/07/04 07:44 AM
06/07/04 07:44 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Hi there cephus,
Welcome to ECN!.
Sounds to me like there is a voltage spike problem, or at the least, a very unstable voltage coming from the generator.
Is there any way that the output can be measured during start-up?.
Failing that, I'd say use some sort of Surge Diversion equipment, could help with the problem.
In the pumps themselves, a type of MOV (metal-oxide-varistor), keeping in mind, that any equipment installed in potentially explosive atmospheres, needs to be rated accordingly!.
Only properly trained persons (petro-chem technicians) should attempt this, I'm telling you!.
Can anyone tell me, are fuel pumps fed by Intrinsically Safe circuits?
Considering they have Fluorescent lights in them.

Re: Generators #38973
06/07/04 08:16 AM
06/07/04 08:16 AM
C
cephus  Offline OP
Junior Member
Joined: Jun 2004
Posts: 2
Pikeville, ky, us
Thanks for the advice about correcting the generator problems. I thought that a buck-boost transformer might eliminate the problems with surges or low voltage occurrences but I didn't think about the harmonics problem. The motors of the pumps might eliminate some harmonics but the circuit boards are definitely seeing some kind of problem.
Do you know of any suppliers that would have a reasonably low cost protection for both the voltage variances and harmonic problems?

I'm not sure there is a MOV on the supply of the circuit boards. If rated correctly, this would eliminate spikes but not the harmonics. Maybe I could place a MOV at the buck-boost transformer, away from the gas pumps.

Re: Generators #38974
06/07/04 10:18 AM
06/07/04 10:18 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,917
Brick, NJ USA
Cephus:
A buck-boost xfr will NOT solve fluctuating voltage problems, and may/could cause additional bad situations. Dependent on the actual load of the circuit that the electronics are on, a good thing may be a "good" UPS unit.

As to the voltage problems, you, or someone, has to stabilize the gen output. In the 'old days', before 'electronics, the gas pumps had no desires for a good 'clean', stable power source, but today it's another story.

John


John
Re: Generators #38975
06/07/04 04:52 PM
06/07/04 04:52 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
It is possible that the generator is not intended for “smooth” motor starting. The inrush current for most single-phase motors is usually of poor power factor and much greater than the steady-state {nameplate} value.

I would try loading the generator with a purely resistive load—like incandescent lamps—piecemeal approaching the rated load a little at a time. A voltmeter should reflect what you may also see in lamp brightness. That may get you started on resolving the problem. I would not invest in an outboard voltage regulator like a Sola transformer—the results will probably be disappointing. A larger generator, purchased with a guarantee that it will have adequate capacity—may be the only effective solution.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9846 MB (Peak: 1.1380 MB) Zlib enabled. Server Time: 2018-01-18 23:28:31 UTC