#38947 - 06/06/04 07:28 PM Sub panel  
oc-nj 08757  Offline
Member
Joined: Jun 2004
Posts: 13
Manchester Twp. NJ
I have someone who wants me to put a 100amp sub panel in their basement. There is already a piece of number 2 SEU running from the main panel to where he wants the sub panel which is not being used for anything. Is there anything I can do to get an additional conductor over or do I need to rip out the SEU and replace it with SER? Any ideas would be appriciated...


Work Gear for Electricians and the Trades

#38948 - 06/06/04 09:17 PM Re: Sub panel  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
You do not need to rip out the SE, but you will need 4 conductors to the subpanel, 2 ungrounded, one grounded, and one equipment grounding conductor. All of them installed in the same raceway or cable.

Pierre


Pierre Belarge

#38949 - 06/06/04 11:20 PM Re: Sub panel  
Attic Rat  Offline
Member
Joined: Dec 2003
Posts: 524
Bergen Co.,N.J. USA
... You NEED to run SER,...it has 2 phase conductors,a neutral,and a ground...anything less than this is a Code violation..also, DO NOT bond the sub-panel's green ground screw to the enclosure..a separate grounding bar is needed here..
Russ


.."if it ain't fixed,don't break it...call a Licensed Electrician"

#38950 - 06/07/04 05:27 PM Re: Sub panel  
oc-nj 08757  Offline
Member
Joined: Jun 2004
Posts: 13
Manchester Twp. NJ
Thanks for the reply's. I've done a ton of these, but I was hopeing to save some $$$ on the wire by finding a legal way to run only 1 conducter instead of buying the SER since there is already a piece of SEU going to where I want to be.



Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7590 MB (Peak: 0.8923 MB) Zlib enabled. Server Time: 2017-07-28 04:39:42 UTC