#38453 - 05/23/04 05:56 PM Faulty Neutral-Sine Wave  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I had an emergency call yesterday. The homeowner was having trouble with dimming lights (with motor surges---much more than normal)and a gas dryer with electronic controls wouldn't start.

I was getting voltage readings within norm, when the POCO guy came. I told him I suspected a neutral problem. He put the phases under load, which showed an imbalance. He said anytime a voltage reading in single phase varies more than 4 volts (L1-N, L2-N)it's probably a faulty neutral.

The homeowner asked why the lights dimmed and he described the current flow in a sine wave with a faulty neutral (using his finger on the wall). Not exactly something I'd try with a homeowner.

Anyway, can anyone explain this clearly or show a diagram of how this changes the current flow? He seemed to be saying that since the neutral was faulty the current came back on itself causing the lights to dim and brighten.

Dave


Work Gear for Electricians and the Trades

#38454 - 05/25/04 05:03 PM Re: Faulty Neutral-Sine Wave  
Mean Gene  Offline
Member
Joined: Oct 2003
Posts: 152
Ohio, USA
Dave,

Sorry for the long delay. It took me a long time to find what I was looking for, and I've been rather busy lately.

The thread listed below contains the best, most comprehensive and easy to understand explanation for what happens when neutral is lost. Makes much more sense than the POCO guy's explanation with a sine wave. It's even better than I have read in most books! [Linked Image]

https://www.electrical-contractor.net/ubb/Forum1/HTML/003640.html

[This message has been edited by Mean Gene (edited 05-26-2004).]


#38455 - 05/25/04 05:25 PM Re: Faulty Neutral-Sine Wave  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
Thanks, Mean Gene. This makes a lot more sense to me now.

Dave


#38456 - 05/26/04 09:10 PM Re: Faulty Neutral-Sine Wave  
CRW  Offline
Member
Joined: Feb 2001
Posts: 159
Bethlehem, PA USA
That IS an excellent thread and explanation. I've been involved with this scenario a couple times and learned what NOT to do! Basically, don't tie in a multi-wire circuit or part of one (any circuit sharing a neutral) while more than 1 leg is still on. Better yet, turn the whole group off. I was forced at the time to work for speed, and not allowed to shut anything down. When the neutral splice came apart (Surprise!) office equipment started leaking smoke and there was alot of screaming and pandemonium.

A friend of mine recently got his service upgraded, and the electrician showed him that his utility neutral had been completely unattached, probably for many years! The current must have been flowing through the waterpipe ground, because they never had any noticeable problems with their power.



Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7604 MB (Peak: 0.8913 MB) Zlib enabled. Server Time: 2017-07-23 08:36:39 UTC