#38273 - 05/19/04 09:56 PM Dry Transformer Primary & Secondary Conduits  
master66  Offline
Member
Joined: Apr 2002
Posts: 257
Masontown, PA, USA
Tell me if there is any problem with the following methods of running conduit to a dry type transformer.

Transformer is sitting on a concrete floor. The primary and secondary conduits are brought directly up into the bottom of the transformer using the proper box connector.

Same situation but stubbing PVC in to the bottom of the transformer with no connector.

Transformer is sitting on floor or hung. A small section of trough or a properly sized pull box is mounted to the side of the transformer where the conductors enter the transformer via chase nipples. The primary and secondary conduits are directly connected to the trough or pull box with no flex. (I know flex is not required)

We were discussing these methods at work today and I'm not sure if there is anything wrong with any of the above methods or not.

They all seem OK although I'm not crazy about stubbing the PVC into the transformer without a connector.

I've always fed the transformer via flex. Just seemed like the easiest way but it can get expensive.

What do you guys think?


Work Gear for Electricians and the Trades

#38274 - 05/19/04 09:59 PM Re: Dry Transformer Primary & Secondary Conduits  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
PVC with no connector would violate 300.4(F), if the conductors are 4 AWG or larger.


Ryan Jackson,
Salt Lake City

#38275 - 05/19/04 10:13 PM Re: Dry Transformer Primary & Secondary Conduits  
elektrikguy  Offline
Member
Joined: May 2002
Posts: 132
woodstock,ga,usa
You could stub up with pvc and put a coupling so that the top is flush with the bottom of the transformer. Then you could use an adapter like the one pictured on page 15. You would not have to lift over threads and risk damaging them. Just shimmy the unit to line up the knock-out that you had made and slide the adapter on. Low profile and allows immediate bending if conductors.
http://www.beckmfg.com/pricesheets/pvc082.pdf


#38276 - 05/19/04 10:49 PM Re: Dry Transformer Primary & Secondary Conduits  
master66  Offline
Member
Joined: Apr 2002
Posts: 257
Masontown, PA, USA
Ryan,

I was always under the impression that bushings were not required with PVC conduit.


#38277 - 05/19/04 10:51 PM Re: Dry Transformer Primary & Secondary Conduits  
fla sparkey  Offline
Member
Joined: Aug 2002
Posts: 47
Winter Haven, Florida USA
Trust me, they are #4 and larger.


#38278 - 05/19/04 10:52 PM Re: Dry Transformer Primary & Secondary Conduits  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I was too. In fact, I couldn't tell you how many times I've installed like this into the bottom of an MDP or MCC.

I hate to say it, but there is no exception for RNC to that rule. [Linked Image]


Ryan Jackson,
Salt Lake City

#38279 - 05/19/04 11:17 PM Re: Dry Transformer Primary & Secondary Conduits  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
.

[This message has been edited by Ryan_J (edited 05-20-2004).]


Ryan Jackson,
Salt Lake City

#38280 - 05/20/04 12:11 PM Re: Dry Transformer Primary & Secondary Conduits  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
352.46 Bushings.
Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.


Don(resqcapt19)

#38281 - 05/20/04 05:56 PM Re: Dry Transformer Primary & Secondary Conduits  
master66  Offline
Member
Joined: Apr 2002
Posts: 257
Masontown, PA, USA
OK, I understand the bushing issue but what about the methods that I described?


#38282 - 05/20/04 06:03 PM Re: Dry Transformer Primary & Secondary Conduits  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
As long as you get some bushings on the PVC method all of the ways you describe are fine.

I have come up in the bottom, used flex, trough, EMT, etc.

As long as you come in where the instructions allow, usually below the terminals.


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.8082 MB (Peak: 0.9805 MB) Zlib enabled. Server Time: 2017-04-26 21:32:03 UTC