Rooftop unit follow-up #36498
04/08/04 07:03 AM
04/08/04 07:03 AM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Is it OK to mount the disconnect on the rooftop unit? I think it is a bad idea, even if permissible. But, there is no existing mounting rack on the roof, and fabricating one would mean securing it to the roof, which would potentially cause leaks in the future.

Thanks,

John

Work Gear for Electricians and the Trades
Re: Rooftop unit follow-up #36499
04/08/04 08:07 AM
04/08/04 08:07 AM
B
Bomzin  Offline
Member
Joined: Mar 2004
Posts: 28
Utah
Yes it's ok, usually mounted right on the unit itself. Why would it be a bad idea, worse idea not to have one.

Bomzin

Re: Rooftop unit follow-up #36500
04/08/04 09:49 AM
04/08/04 09:49 AM
M
Mean Gene  Offline
Member
Joined: Oct 2003
Posts: 152
Ohio, USA
I think John's reasoning for it not being a good idea is in the event the chassis of the unit were to become energized or the unit were to catch fire the disco may become untouchable.

Re: Rooftop unit follow-up #36501
04/08/04 10:11 AM
04/08/04 10:11 AM
A
Anonymous
Unregistered

Not that it makes it right or wrong but I have mounted a gazillion disco's to RTU's.
Mounted directly to the unit on large units and various strut set-ups on others. The only issues I have had are: Do not mount to access covers. Do not mount over name plates. Do not screw into internal coils [Linked Image].

Re: Rooftop unit follow-up #36502
04/08/04 11:07 AM
04/08/04 11:07 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
440.14


Ryan Jackson,
Salt Lake City
Re: Rooftop unit follow-up #36503
04/08/04 06:15 PM
04/08/04 06:15 PM
D
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
When I worked at a local grocery store chain, I remember seeing several disco's mounted towards the corner of the units - the idea being, if the case becomes "hot", one can D/C the power by using a hot stick / "broom" stick, or other nonconductive means.

The D/C is also visible from 2 sides, and I've seen the units labeled with yellow and black "caution" style labels as to where the D/C's were, as well as information as to which panel they were being fed from.

Not a code requirement, of course, but a good idea nontheless.

Re: Rooftop unit follow-up #36504
04/08/04 06:25 PM
04/08/04 06:25 PM
T
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Kentvw said it best. Follow those directions and you can't go wrong.

If you wire/ground correctly, how can the "case" become hot? If it is not wired correctly then no procedure for disconnect placement is going to make the set-up safe.

Re: Rooftop unit follow-up #36505
04/08/04 06:35 PM
04/08/04 06:35 PM
M
maintenanceguy  Offline
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
Triple beat me to it. If everything's grounded properly, the disconnect's housing would be hot if the RTU cabinet was no matter how far away it was mounted.

And if it's right on the unit, The HVAC guy (That's usually me) never has to wonder if he's turned off the right switch. And do us a favor, mount your switch right above the equipment's data plate. When they're exposed to the sun and rain they fade so bad we can't read them but everytime I see a data plate under the disco, the plate looks like the day it was made. [Linked Image]

Re: Rooftop unit follow-up #36506
04/08/04 06:37 PM
04/08/04 06:37 PM
T
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
I do, however, like to mount the disconnect separate from the unit to facilitate that units removal/replacement in the future. Most of the time this is not very practical without a good deal of additional labor. Thus the disco gets screwed to the side of the rooftop unit.

Re: Rooftop unit follow-up #36507
04/08/04 06:48 PM
04/08/04 06:48 PM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I was thinking in terms of replacing the condensing unit, and having the disconnect flopping around on the ground in the meantime.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 13
Popular Topics(Views)
243,542 Are you busy
180,344 Re: Forum
170,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.035s Queries: 15 (0.012s) Memory: 1.0201 MB (Peak: 1.1959 MB) Zlib enabled. Server Time: 2018-01-19 01:45:08 UTC