stub ups #36423
04/06/04 05:29 PM
04/06/04 05:29 PM
B
big guy  Offline OP
Member
Joined: Dec 2003
Posts: 59
pa
Dose anybody know where i can get sizes
for rigit pipe stub ups. From 2" to 5"
thanks alot big guy

Work Gear for Electricians and the Trades
Re: stub ups #36424
04/06/04 06:06 PM
04/06/04 06:06 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
Are you looking for 90 deg elbows? Your supply house should handle at least through 4" and be able to order larger.

-Hal

Re: stub ups #36425
04/06/04 07:30 PM
04/06/04 07:30 PM
C
cavo148  Offline
Member
Joined: Jan 2004
Posts: 79
New Jersey
Hal is right about getting 90 degree sweeps, or manufactured 90's as some call them, from your supplier. If you want to save some money, down the road that is, next time you come across another EC with a hydraulic pipe bender make some sort of a deal with him. I'm sure he'll be happy to make a few extra bucks to cover the cost of his bender. At the very least, it'll be one less big coupling you have to buy.

Andy

Re: stub ups #36426
04/10/04 11:23 AM
04/10/04 11:23 AM
B
big guy  Offline OP
Member
Joined: Dec 2003
Posts: 59
pa
thanks i got it
we have some big benders that i use but thay
are not on my job.I have to put in pipes from one room to another.(under the slab) One room is 18" higher i can't have the bend
of the pipes stick out of the slab per spec.

Re: stub ups #36427
04/11/04 07:02 PM
04/11/04 07:02 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
I assume the pour is not on grade where you could just trench deep enough so the bend will be below the finished floor. The way around this is to use two 45 deg bends, one horizontal and the other vertical. Align both so the stub up is plumb. Hopefully this will keep everything below.

-Hal


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 14
Popular Topics(Views)
243,554 Are you busy
180,360 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.9651 MB (Peak: 1.1051 MB) Zlib enabled. Server Time: 2018-01-20 00:54:04 UTC