8/2 UF #35978
03/25/04 10:39 PM
03/25/04 10:39 PM
A
Anonymous OP
Unregistered

Has anyone seen 8/2(with ground) UF? I can find 8/3 in UF but only 8/2 in NM.
Thanks, Brian

Work Gear for Electricians and the Trades
Re: 8/2 UF #35979
03/25/04 10:51 PM
03/25/04 10:51 PM
M
Merlin  Offline
Member
Joined: Jan 2004
Posts: 171
NW Indiana
Brian

8/2 UF with ground is available at www.gesupply.com . The part number is 8-2 WG UF RL. I have never used any but it is in my catalog.

Kevin

Re: 8/2 UF #35980
03/26/04 04:30 AM
03/26/04 04:30 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Brian, can I ask what you are feeding with the 8/2?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 8/2 UF #35981
03/26/04 09:28 AM
03/26/04 09:28 AM
A
Anonymous OP
Unregistered

Thanks Merlin.
Iwire, it's for a 30A 120V RV hookup. The run is too long for #10.
Brian

Re: 8/2 UF #35982
03/26/04 04:34 PM
03/26/04 04:34 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Brian if you have a sharp inspector they will notice that grounding conductor is to small.

250.122(B) requires the grounding conductor size to be increased when the other conductors are increased for any reason.

In the case of a 30 amp circuit you need a full size grounding conductor, run 8 AWG hot & neutral and you need a 8 AWG ground.

You might want to use the 8/3 and ask the inspector if he has a problem with remarking the red to green or just stripping the red to bare.

Good luck, Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 8/2 UF #35983
03/27/04 07:18 AM
03/27/04 07:18 AM
S
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
I've never priced 8/2 cable, but would not 8/3 be cheaper as its much more common? Just a thought.

Re: 8/2 UF #35984
03/27/04 08:28 PM
03/27/04 08:28 PM
A
Anonymous OP
Unregistered

Thanks for the replies. I never thought about the grounding conductor. Guess I'll ask the inspector first, if he balks it will be time for pipe and THHN/THHW.
I've always wondered about re-marking a red, white or black conductor as a grounding conductor and in fact I've done it on occasion however there were no inspections.
What are most AHJ's position on this?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,554 Are you busy
180,360 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9767 MB (Peak: 1.1305 MB) Zlib enabled. Server Time: 2018-01-19 22:54:21 UTC