#35380 - 03/10/04 11:42 AM California 3-way  
Anonymous
Unregistered

Years ago we would wire 3-ways using two conductor cable only and you would end up with a hot and neut in both 3-ways. One two wire from each 3-way to the light and one two wire between the three ways. This was called a "California" System. However I don't remember the connections. Can anyone provide a diagram or tell me where I can find one. Thanks


Work Gear for Electricians and the Trades

#35381 - 03/10/04 11:54 AM Re: California 3-way  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
You may also hear this called a 'French three way', 'Carter three way' or an 'illegal three way'. By whichever name you use, it is illegal and dangerous. The system switches the neutral, which is a clear violation of the NEC. Additionally, on one of the 'off' positions the lamp is still 'hot', with both the screw shell and the center pin 'hot' so that there is no voltage between them.

They way that it works is that you use the three way switches _fed_ from the traveller terminals, with the common terminal connected to the lamp. If one three way is switched so that its common is connected to hot, and the other three way is switched so that its common is connected to neutral, then you complete the circuit and the lamp lights. If both switches present neutral to the lamp, then the lamp is off and everything is safe. If both switches present hot to the lamp, then the lamp is off, but everything is energized to line voltage.

Take a look at http://www.geocities.com/gary_wachs/ElectriPuzzles.html for some interesting three way circuits.

-Jon


#35382 - 03/10/04 01:52 PM Re: California 3-way  
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
Also called the "Chicago 3-way too". Whatever you call it its illegal and dangerous. [Linked Image]


John

#35383 - 03/10/04 05:36 PM Re: California 3-way  
Anonymous
Unregistered

I tried to post a sketch as a photo but can't figure out how to do that although I have seen it done on other posts...hhmmm.
OK here's the wiring and the neutral is not switched. Took a while to figure this out.
There is a two conductor from each switch to the light and a two wire between the two three ways. The black in the two wire between the switches carries the hot through and ties to a traveller post on each switch. The white in the same wire ties to the common on each switch. The white from each two wire carries the neutral through and both tie to the light.
The black in the same wires both tie to the light and to the other traveler on each three way. Feed this set-up on either end and you end up with a hot and neut on the other end. If this goofy set up doesn't meet code why? Appologies in advance if this has been discussed before.


#35384 - 03/10/04 06:18 PM Re: California 3-way  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Thanks, Kent.

Your description answered a question I've had about this scheme since I first heard of it way back. I never could quite visualize it. What I had missed is that the neutral goes off through the light while the hot heads toward the other 3-way. Bringing the neutral to the far 3-way, thus enabling the continuing of the branch circuit is a nice touch.

The polarity at the lampholder is always correct.

The downside, for me is the unbalanced magnetic field created in some switch settings, or when the branch is continued and downstream load is connected. But that is a health issue (and debated, at that), not a NEC issue.

Bottom line, what you described is NEC compliant, IMO.

This is my idea of what you described, KentVW:


[Linked Image]

ElectricAL

[This message has been edited by Webmaster (edited 03-10-2004).]


Al Hildenbrand

#35385 - 03/10/04 07:57 PM Re: California 3-way  
:andy:  Offline
Member
Joined: Oct 2003
Posts: 289
Germany
the circuit #3 is known as the "american alternating circuit" here. it's prohibited because the fixture can be hot when the light is off...


#35386 - 03/10/04 08:36 PM Re: California 3-way  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
ElectricAL points out the problem with this circuit. Depending upon switch setting or downstream load, your current flows in a large loop, going (in the diagram) from 'switch left' to 'switch right', then 'up' to the lamp, then down to 'switch left'. I believe that this violates 300.3(B), because all the conductors for the circuit are not present in the same cable.

-Jon


#35387 - 03/10/04 09:02 PM Re: California 3-way  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
:andy,

In this case the conductor that's always in contact with the fixture is the grounded one. There is a another 3-way arrangement that you are probably thinking of.

Bill

(psst; nice picture Al -- [Linked Image] )

[This message has been edited by Bill Addiss (edited 03-10-2004).]


#35388 - 03/10/04 09:47 PM Re: California 3-way  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
I do some work for a builder who also sell mod. homes.The factory wires the fixtures 'hot'at top of basement stairs and bottom of attic stairs,with 3-wire to switch,and 3-wire drops for site installed 3-way.I've been changing them to 'hot at switch' but that's a pain,and time eater;I'd love to site code section to builder to feed-back to modular mfr. to end this.What is it ?


#35389 - 03/10/04 09:58 PM Re: California 3-way  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Jon,

I think 300.3(B)(3) provides the exception that results in the setup in the diagram that I drew to be NEC compliant. The common installation would be in a dwelling wired with NM-B.

Al


Al Hildenbrand

Page 1 of 2 1 2

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.8154 MB (Peak: 0.9905 MB) Zlib enabled. Server Time: 2017-07-21 04:49:11 UTC