Jacuzzi electrical rating? #34927
02/28/04 11:15 AM
02/28/04 11:15 AM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
In general, what is the typical rating of a residential bathroom jacuzzi? 120 or 240? Amps?
As far as the NEC is concerned I would classify that as a hydromassage tub. Am I correct?

Frank

Work Gear for Electricians and the Trades
Re: Jacuzzi electrical rating? #34928
02/28/04 11:31 AM
02/28/04 11:31 AM
W
watthead  Offline
Member
Joined: Oct 2001
Posts: 172
South Carolina
Frank
The ones I have connected have been mostly 120v with a 20 amp cord connection.

Re: Jacuzzi electrical rating? #34929
02/28/04 11:39 AM
02/28/04 11:39 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Frank,

Nice to hear from you.

As Jacuzzi is a brand name this could be confusing. If it has a heater I'd call it a Spa or Hot Tub. If it's just a Pump with jets then it's a Hydromassage tub.

I've never seen a 240v hydromassage tub. Typical ratings are 15A or 20A @ 120v

Bill

Re: Jacuzzi electrical rating? #34930
02/28/04 11:44 AM
02/28/04 11:44 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I agree with everyone else, but I would like to add that I see them above 1/2HP on a regular basis. With that in mind, they are required to be on their own circuit.

430.148, 210.23(A)(2)


Ryan Jackson,
Salt Lake City
Re: Jacuzzi electrical rating? #34931
02/28/04 12:44 PM
02/28/04 12:44 PM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Thank you. Excellent information as usual.

Re: Jacuzzi electrical rating? #34932
02/28/04 12:53 PM
02/28/04 12:53 PM
A
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
We allways run a 20 amp 120v circuit. We did a feew larger ones do require (2)120v circuits because they have seperate pumps and cords that draw too much for (1) 20 amp circuit. I don't remember too many with heaters but I guess that would be a circuit too.

We always put the GFI in the panel. A few places here require that so we do them all that way. Did some that the noodel was shared and the GFI protection was in the bathroom. Having to go back and put it in the panel for the inspector is a big hassel.

This area uses EMT but some towns also want a ground wire pulled from the panel. I don't do that unless I know it is required but I allways leave space in the pipe just in case. Dose anyone pull a ground wire to the tub thru EMT if it's not asked for?

I also see some companies use outdoor bell boxes, compression connectors, etc. to keep things dry. I think that is a bit much but does anyone elce do that? I will keep the box under the tub off the floor with a board but thats it.

Tom

Re: Jacuzzi electrical rating? #34933
02/28/04 02:43 PM
02/28/04 02:43 PM
U
u2slow  Offline
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
The last few I wired I used a blank-face GFI and a toggle switch for a disconnect. (On its own circuit of course.)

Re: Jacuzzi electrical rating? #34934
02/28/04 04:01 PM
02/28/04 04:01 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Active 1 raises a good point. If the water is chlorinated, it {and its vapors} are especially good a dissolving the galvanizing on EMT and the steel underneath. My pre-retirement employer {research facility} required a copper equipment ground in all raceway runs—period. One problem with older electrical components was that ready attachment of the grounding conductor was not always available—you got good at using cutting oil and a 10-32 tap chucked in a drill motor, with the requisite star lockwasher between the enclosure and grounding-conductor attachment.

Re: Jacuzzi electrical rating? #34935
02/28/04 04:14 PM
02/28/04 04:14 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
On another forum this was posted by someone that owned a Jacuzzi tub, they claimed this was what the instructions said.

Quote

MOTOR/PUMP: 115 VAC, 3450 RPM/7.8 AMP, 60 Hz Single phase.

ELECTRICAL SERVICE REQUIREMENTS:

115 VAC, 15 AMP, 60 Hz. Requires dedicated separate circuit.


Given this infomation would it be correct to feed it with a 20 amp circuit?


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Jacuzzi electrical rating? #34936
02/28/04 04:25 PM
02/28/04 04:25 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I wonder why it doesn't give the horsepower rating?


Ryan Jackson,
Salt Lake City
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,400 Re: Forum
170,867 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.036s Queries: 15 (0.020s) Memory: 1.0231 MB (Peak: 1.1993 MB) Zlib enabled. Server Time: 2018-01-23 06:02:14 UTC