Emergency / Exit fixtures #34320
02/08/04 02:53 PM
02/08/04 02:53 PM
G
gzgerson  Offline OP
Junior Member
Joined: Feb 2004
Posts: 2
Phila, Pa
Hello

I'm new here and have a question on "Emergency / Exit fixtures". Our one story cement block building in Philadelphia Pa has exit signs in each office/room (no windows in offices or meeting rooms). The Exit fixtures are all on one breaker (great for annual battery testing).

After a recent power outage we decided to add emergency lighting in each room. Two ECs
have suggested we replace the "Exit fixtures" with "Exit / Emergency combo fixtures".

One EC said just replace the "Exit fixtures" with "Exit / Emergency combo fixtures", the other EC said they should be wired to the lighting circuit of each room (in case the breaker for that room trips). They both said their proposal was code compliant.

Which one is code compliant?

Thanks for the help:
George


[This message has been edited by gzgerson (edited 02-08-2004).]

[This message has been edited by gzgerson (edited 02-08-2004).]

Work Gear for Electricians and the Trades
Re: Emergency / Exit fixtures #34321
02/08/04 03:16 PM
02/08/04 03:16 PM
L
LK  Offline
Member
Joined: Jan 2003
Posts: 1,429
New Jersey
George,
Good question, You should put them on the lighting circuit for the area served, ahead of any switches, However there is an exception and I do not have the code book here, so I can't comment, there are others on line, that I am sure will be able to help.

Re: Emergency / Exit fixtures #34322
02/08/04 03:18 PM
02/08/04 03:18 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
There are many ways to gain compliance, but the most common way is to install the E-circuits with the general purpose lighting. A dedicated circuit is permitted, but it must be on a generator or other type of uninteruptalbe supply. Refer to 701.11, and you will see that the same circuit is probably the cheapest/easiest way.


Ryan Jackson,
Salt Lake City
Re: Emergency / Exit fixtures #34323
02/08/04 04:25 PM
02/08/04 04:25 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
They are both right, kind of, in an open area with 3 or more lighting circuits the emergency battery units may be on a dedicated circuit.

Otherwise the EBUs must be on the lighting circuit feeding the area the EBUs are located in.

Part of 700.12(E) and it's exception.
Quote
700.12(E)........The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches. The branch circuit that feeds unit equipment shall be clearly identified at the distribution panel. Emergency luminaires (illumination fixtures) that obtain power from a unit equipment and are not part of the unit equipment shall be wired to the unit equipment as required by 700.9 and by one of the wiring methods of Chapter 3.

Exception: In a separate and uninterrupted area supplied by a minimum of three normal lighting circuits, a separate branch circuit for unit equipment shall be permitted if it originates from the same panelboard as that of the normal lighting circuits and is provided with a lock-on feature.


[This message has been edited by iwire (edited 02-08-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Emergency / Exit fixtures #34324
02/08/04 04:40 PM
02/08/04 04:40 PM
B
big guy  Offline
Member
Joined: Dec 2003
Posts: 59
pa
Exception: In a separate and uninterrupted area supplied by a minimum of three normal lighting circuits, a separate branch circuit for unit equipment shall be permitted if it originates from the same panelboard as that of the normal lighting circuits and is provided with a lock-on feature .

ok what is it a standby systems or a emergency systems
the same thing is in 701.11 (f)

Re: Emergency / Exit fixtures #34325
02/09/04 12:37 AM
02/09/04 12:37 AM
G
gzgerson  Offline OP
Junior Member
Joined: Feb 2004
Posts: 2
Phila, Pa
Thanks for all your input. I will check the # of lighting circuits for each area and have the fixtures wired accordingly.

regards:
George


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,587 Are you busy
180,382 Re: Forum
170,859 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.005s) Memory: 0.9760 MB (Peak: 1.1203 MB) Zlib enabled. Server Time: 2018-01-22 02:19:07 UTC