#34295 - 02/07/04 01:40 PM Lighting Dimmer Packs  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Regarding the church I am upgrading wiring on is the lighting dimmer pack calls for 2-20 amp at 120v circuits input, and 4-channels output at 1200 watts 120v each. That output would seem to be a bit high for just 2-20a circuits?


The Golden Rule - "The man with the gold makes the rule"

Work Gear for Electricians and the Trades

#34296 - 02/07/04 05:04 PM Re: Lighting Dimmer Packs  
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
The lighting would be considered a continuous load so each 20A circuit would be limited to 1920watts or 3840 watts for two.


John

#34297 - 02/08/04 01:09 PM Re: Lighting Dimmer Packs  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
electricman2,
It seems that the 1200 watts per channel (2 channels per circuit) would put it at 2400 watts output, over the 1920 watts, right?


The Golden Rule - "The man with the gold makes the rule"

#34298 - 02/08/04 01:27 PM Re: Lighting Dimmer Packs  
N.O.Minded  Offline
Member
Joined: Jan 2002
Posts: 10
Pensacola,FL-USA
Perhaps if these dimmers were fed via breakers listed for 100% continuous load?


#34299 - 02/10/04 05:57 PM Re: Lighting Dimmer Packs  
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
I don't know how the system is set up. It may be possible to split it up into 3 circuits.


John

#34300 - 02/10/04 07:57 PM Re: Lighting Dimmer Packs  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
You are going to have to double check the data/instruction sheet for the dimmer packs. It may very well be that they are rated for 1200W per channel, 4 channels, but at less than 3600W _total_ output at any one time. Or it may be the case that being on a dimmer pack lets one consider the lighting 'non continuous'...or it may be the case that the dimmer pack has a built in controller that limits the output power to be less than 3600W for > 3 hours. Or it may be an error in the listing.

I would certainly double check prior to putting the dimmer pack on OCPD > the 20A listed in the instructions. It is possible that the unit is listed only for use on a 20A circuit.

-Jon


#34301 - 02/11/04 09:54 AM Re: Lighting Dimmer Packs  
Mike Wescoatt  Offline
Member
Joined: Jun 2001
Posts: 161
Cedar City, Utah
Check out the listing and instructions since many dimmers are indeed rated for 100% of their rated load. Also, since these sound like thyrister based dimmers you may also need to install a 200% neutral. Check out NEC section 520 for the details.


Mike Wescoatt

#34302 - 02/11/04 11:05 AM Re: Lighting Dimmer Packs  
strangedog  Offline
Member
Joined: Aug 2002
Posts: 35
Dayton, Ohio
What kind of dimmer pack is this? I sounds like one of the el cheapo dj models. The instructions read, "Just plug it into to different outlets on different breakers and you are good to go!" If you are modifing it for fixed wiring you are probally violating it's listing (if it is not an unlisted taiwan knockoff).

Most dimming kit has OCPD rated at 100% with the assumption that in a large installation that all dimmers are not pulling 100%. For example a 96 dimmer rack with 20 amp dimmers can be feed from a 400amp three phase service as per the manufacturer.

As for your dimmer, if you open it and take a look, it is two seperate devices. Each 20 amp dimmer has a scr or two, a couple of chokes and a firing circuit. Technically, you could load the each dimmer up to 100%, but if you plan to do this full time the entire installation needs to support it (100%rated OCPD in the pannel). Do not put bigger breakers in the pannel, stick with the 20amps.

SD

SD


SD
It is best for a leader to be both feared and loved. But since this usually cannot be done, it is safer to be feared.


Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7920 MB (Peak: 0.9531 MB) Zlib enabled. Server Time: 2017-05-26 22:44:23 UTC