#33663 - 01/27/04 10:55 AM CAT 5 voltage rating?  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
I would like to use CAT 5 cable for lowvoltage (24) volt control wiring.
I am planning to control 3Amp contact rating relays to operate window shutters. And am planning on using small N/O switches to control the relays.

Is the rating of the CAT 5 cable higher than 24 Volts?


Any other suggestions?


Edward


Thanks
Edward

Work Gear for Electricians and the Trades

#33664 - 01/27/04 12:44 PM Re: CAT 5 voltage rating?  
C-H  Offline
Member
Joined: Sep 2002
Posts: 1,497
Stockholm, Sweden
Check the cable. I had a look at some of the patchcords in the office: 300V (sic!)

The other rating I commonly find on computer cables is 30V. I think it would be technically impossible to manufacture a cable that could not handle this.


#33665 - 01/27/04 06:47 PM Re: CAT 5 voltage rating?  
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
CAT5 as well as any of the other CAT cables are CL2 listed and as such are 150V. You will be fine.


#33666 - 01/27/04 10:18 PM Re: CAT 5 voltage rating?  
BrianSparky  Offline
Member
Joined: Jan 2002
Posts: 38
Lakewood,CO
Just as a suggestion...
try using 18 gauge control wire.
phone wire is only about 22 gauge.


#33667 - 01/27/04 10:42 PM Re: CAT 5 voltage rating?  
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
I second Brian's suggestion for 18awg. Volt drop becomes an issue very quickly when you are starting with low voltage.

GJ


#33668 - 01/28/04 01:15 AM Re: CAT 5 voltage rating?  
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
That was my first thought also but after rereading the question I think I understood that the 24ga wire will operate the coils of the relays through the switches. Not much current there so voltage drop shouldn't be a problem. The 3A current rating is for the relay contacts, not the current through the control wire.


#33669 - 01/28/04 02:46 AM Re: CAT 5 voltage rating?  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
Thanks for the reply.

The contact rating is 3 amps.

The voltage problem should not be a problem. I just need to verify that using a CAT 5 cable is an acceptable method in this application which sounds like it is. And i am not violating NEC.

Edward


Thanks
Edward

#33670 - 01/29/04 12:18 AM Re: CAT 5 voltage rating?  
ComputerWizKid  Offline
Member
Joined: Sep 2003
Posts: 119
Connecticut, USA
Last time I checked 5 mins ago cat 5E is 26 Guage Might want to get 20 or 18 Guage wire


Theres always enough room in the junction box.You just need a bigger hammer

#33671 - 01/29/04 12:32 AM Re: CAT 5 voltage rating?  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
It is 24AWG. I think i will use thermostat wire 18AWG.

Edward


Thanks
Edward

#33672 - 01/29/04 12:52 AM Re: CAT 5 voltage rating?  
ComputerWizKid  Offline
Member
Joined: Sep 2003
Posts: 119
Connecticut, USA
The stuff I have is 26 AWG it came with my cable modem. but the newer stuff is 24 Guage


Theres always enough room in the junction box.You just need a bigger hammer

Page 1 of 2 1 2

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.002s) Memory: 0.8149 MB (Peak: 0.9886 MB) Zlib enabled. Server Time: 2017-04-27 14:56:16 UTC