hi
i installed a sunhouse storage heater and everything was working fine when i left it, but now the heater has stopped working. there is no voltage at the load side of the thermostat at the top of the heater, but there is at the supply side. i know these things have thermal cutouts but im not sure what im looking for, so i was wondering if somebody had a picture i could get some idea from and how to reset it if its tripped.
many thanks
matt
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Matt, There should be a small resettable switch on the front of the thermostat. This is usually wired between the main feed wire and the line side of the thermostat. Sorry I haven't got a pic to show you, but it should be easy to find, it looks like a small Micro switch. Turn off the supply before resetting it though!.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Matt,
I don't know if it has any bearing here, but it might be worth mentioning that you're in the UK.
Maybe a model name would help to get some specific info.
Bill
Bill
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Matt,
There are different configurations. I've seen storage heaters with a separate thermal cutout wired in series while others have one incorporated in the main thermostat body.
You also have some 'stats which are "open"construction and easy to replace the cutout while others are sealed in and the only practical solution is to replace the whole stat.
|
|
|