#33146 - 01/13/04 04:47 PM wire capacity of 1/2 inch conduit  
cpalm1  Offline
Member
Joined: Jan 2004
Posts: 66
i have a 1/2 inch conduit that runs from my panel to the far side of my house and supplies 2 rooms, a hallway and a garage.
currently this pipe contains three 15 amp circuits and a 20 amp circuit. these are multiwire circuits. there are 4 14 gague wires and 2 12 gauge wires.

could i add an additonal 2 amp circuit? to do this i would need to pull an additonal 12 gauge wire and a 14 gague neutral.

then i would have 4 15 amp circuits and 2 20 amp circuits.

simply put, the pipe would contain 6-14 AWG (4 current carrying) and 3 12 AWG (2 current carrying) would this be ok, or would the pipe be over stuffed?


Work Gear for Electricians and the Trades

#33147 - 01/13/04 05:21 PM Re: wire capacity of 1/2 inch conduit  
George  Offline
Member
Joined: Feb 2002
Posts: 375
It appears that the answer is you can not, but I just did a rough calculation.


#33148 - 01/13/04 05:35 PM Re: wire capacity of 1/2 inch conduit  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
What is the wire type? If it is THHN there is not a problem with the conduit fill or with the ampacity adjustment for more than 3 current carrying conductors.
Don


Don(resqcapt19)

#33149 - 01/13/04 08:25 PM Re: wire capacity of 1/2 inch conduit  
cpalm1  Offline
Member
Joined: Jan 2004
Posts: 66
The wire is THHN


#33150 - 01/13/04 10:52 PM Re: wire capacity of 1/2 inch conduit  
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
Why would you pull a 14 ga. neutral with a 20 ga. hot?


#33151 - 01/13/04 11:01 PM Re: wire capacity of 1/2 inch conduit  
cpalm1  Offline
Member
Joined: Jan 2004
Posts: 66
because the there is a multiwire system in the pipe that has a 20 amp and 15 amp circuit. when i add the second 20 amp, i plan to use the 12 gauge neutral that is already in the box, and pull a new neutral for the old 15 amp ciruit that is currently sharing the old 20 amp circuit's neutral.


#33152 - 01/13/04 11:04 PM Re: wire capacity of 1/2 inch conduit  
cpalm1  Offline
Member
Joined: Jan 2004
Posts: 66
basically i would end up with a total of 5 circuits. there would be 3 15 amp circuits. 2 of them would share a neutral and one would have it's own neutral (the 14 gauge that i am pulling). The new hot 12 gauge would be hooked up to the old 12 gague neutral. of course i would make sure all of the breakers for the multiwire circuits are on opposite 120V legs.



Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.7825 MB (Peak: 0.9327 MB) Zlib enabled. Server Time: 2017-10-18 13:04:59 UTC