Common Neutral Code ? 215.4 in 2002 NEC #33134
01/13/04 03:18 PM
01/13/04 03:18 PM
R
Rob  Offline OP
Member
Joined: Dec 2003
Posts: 15
New York
How many circuits can one neutral share?
#12 stranded wire.
Code wording is unclear to me, it reads -
TWO or THREE sets of 3-wire feeders or TWO
sets of 4-wire or 5-wire feeders.

(Can I share a common neutral with three 20 amp single phase circuits?)Thanks in advance.

Work Gear for Electricians and the Trades
Re: Common Neutral Code ? 215.4 in 2002 NEC #33135
01/13/04 03:33 PM
01/13/04 03:33 PM
C
cpalm1  Offline
Member
Joined: Jan 2004
Posts: 66
on single phase you can share a common neutral with 2 circuits of the same ampacity as the neutral. for example, two 20 amp circuits can share one 12 gauge neutral. The catch is that the 2 circuits must be on OPPOSITE legs of the 240 volt breaker panel. The neutral will only carry the differnece in current between the two circuits. for exampl, if one circuit has a 12 amp toaster on it and the other has a 9 amp coffee maker, the neutral will be carrying 3 amps

Re: Common Neutral Code ? 215.4 in 2002 NEC #33136
01/13/04 05:22 PM
01/13/04 05:22 PM
D
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
Don't forget the requirement of D/C'ing BOTH current carrying conductors with one motion (tied OCPD's) for the circuit in questions.

Re: Common Neutral Code ? 215.4 in 2002 NEC #33137
01/13/04 05:54 PM
01/13/04 05:54 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
Doug, that only applies if the two circuits supply device(s) on one yoke such as split wired duplex receptacles. (210.4) If this is simply a 3 wire home run then a two pole breaker is not required.

Re: Common Neutral Code ? 215.4 in 2002 NEC #33138
01/13/04 06:18 PM
01/13/04 06:18 PM
D
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
You are correct. Thought that the interp. included shared neutrals in general.

Re: Common Neutral Code ? 215.4 in 2002 NEC #33139
01/13/04 06:31 PM
01/13/04 06:31 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Its amazing how mis-interpreted that provision is.


Ryan Jackson,
Salt Lake City
Re: Common Neutral Code ? 215.4 in 2002 NEC #33140
01/13/04 07:25 PM
01/13/04 07:25 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Rob, let's look at your question closely.

First of all 215 is for feeders so we will leave this section and go on to 225.7(B) which will allow you to put as many circuits as you want on a properly sized neutral. Yes this section is specific to "Outside Branch Circuits and Feeders" but there is nothing in any other section prohibiting it for other applications.

If you are using a neutral conductor the same size as the circuit conductors, then you could have a neutral common to both ends of a single winding, (transformer) or common to three windings connected in a wye or star configuration. This goes with Cpalm1's post

I know, I'm causing trouble. [Linked Image]

Roger

[This message has been edited by Roger (edited 01-13-2004).]

Re: Common Neutral Code ? 215.4 in 2002 NEC #33141
01/13/04 08:11 PM
01/13/04 08:11 PM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 785
Oradell NJ USA
Say that there were 4 15 amp circuits sharing one neutral. If 2 circuits come from one side of the supply, and the other two are fed by the other side, then can I use one neutral that is sized to take 30 amps (AWG 10 IIRC)? This would have to be in one conduit I would think.

Re: Common Neutral Code ? 215.4 in 2002 NEC #33142
01/13/04 08:25 PM
01/13/04 08:25 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Wa2ise, yes that would be allowed per 225.7(B)specificaly. Seems strange doesn't it. [Linked Image]

Roger

Re: Common Neutral Code ? 215.4 in 2002 NEC #33143
01/13/04 10:49 PM
01/13/04 10:49 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Roger;

Quote

I know, I'm causing trouble. [Linked Image]


Not even if you tried to! [Linked Image]

Addressed things which are indeed very related to this scope.

I like the descriptions of Transformers, which basically caught my eye - and led to this reply!

To the original poster:

Although the idea of using an oversized Common Grounded Conductor for several multiwire circuits is compliant to the NEC, it still just sounds odd to me!
It works, and should be safe - if installed properly; it's only a "different" method, very much "unthought of" by many of us here - including myself!

Regardless of which option you choose - be sure to have a "Balance" of Ungrounded Conductors which are derrived from Breakers on "Opposite Polarity Points" in the Panel.
Simply, if you can measure 220-240 VAC across two Breakers, use these two circuits for a single multiwire circuit. Step down 1 space from that multiwire for the next one.

BTW: Per the term "Opposite Polarity Points", I use that term because "Opposite Phases" really does not apply to a 1Ø 3W system.

Talk about starting trouble [Linked Image]

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 15
Popular Topics(Views)
243,566 Are you busy
180,366 Re: Forum
170,844 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.003s) Memory: 1.0247 MB (Peak: 1.1998 MB) Zlib enabled. Server Time: 2018-01-20 18:58:54 UTC