Panel Accessibility question... #32405
12/22/03 05:48 PM
12/22/03 05:48 PM
N
NJwirenut  Offline OP
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
Have a customer living in a garden apt. complex. With the permission of apt. management, 3 new 20A circuits for recepts (computer, window A/C, and microwave) were installed.

Since each dwelling unit in this complex has an old 4-hole edison base fusebox and a 60 A feeder from a central utility room, the new lines were taken straight to the utility room, where 3 new breakers were installed in the enclosure that housed the 60A 2-pole feeder breaker that feeds (ONLY) this apartment. Installation passed inspection by local AHJ with flying colors several years ago.

Since the installation was done, apartment management has decided to lock the meter room, rendering the service disconnects for electric, water, and gas to each apartment inaccessible. This includes my 3 new branch circuit breakers, as well as many others that other sparkies have added for other tenants over the years.

Is this lack of access to the service disconnect and branch OCPDs now a NEC violation? 230.72(C) seems to indicate so, unless this falls under the exception, which is vaguely worded. Several tenants are complaining about needing to call maintenance and wait forever for someone to unlock a door in order to reset a tripped breaker or shut off the water when a pipe breaks! [Linked Image]

Work Gear for Electricians and the Trades
Re: Panel Accessibility question... #32406
12/22/03 10:26 PM
12/22/03 10:26 PM
S
stamcon  Offline
Member
Joined: Mar 2001
Posts: 330
So San Francisco CA
I think if the tennants have 24 hour access to the management company, it is legal under the exemption of 230-72(c)(99NEC).


Steve
Re: Panel Accessibility question... #32407
12/22/03 10:46 PM
12/22/03 10:46 PM
N
NJwirenut  Offline OP
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
My question about the exception note is that it refers to "the service disconnecting means supplying more than one occupancy". I interpreted this to mean the MAIN service disconnect ahead of all the individual apartment meters/breakers.

Since there are about 30 or so tenant meters/panels in this room, the "6 or less" provision means that these breakers cannot be considered true "service disconnects" for the building. The main disconnect switch feeding the meter bank is in a separate area that has been locked for many years.

[This message has been edited by NJwirenut (edited 12-22-2003).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,890
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
Potseal 15
sparky 15
Popular Topics(Views)
243,565 Are you busy
180,366 Re: Forum
170,843 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9501 MB (Peak: 1.0729 MB) Zlib enabled. Server Time: 2018-01-20 16:53:31 UTC