ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Correct rotation, wrong sequence
by Potseal. 05/27/17 12:15 AM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
210.70 / Wall Switch / When adopted?
by gfretwell. 05/24/17 09:18 PM
Any UL 508 experts out there?
by sparkyinak. 05/23/17 11:04 PM
Heat pump conundrum
by sparkyinak. 05/21/17 08:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,849 Are you busy
171,859 Re: Forum
164,763 Need opinion
Who's Online Now
0 registered members (), 45 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#31764 - 12/03/03 09:31 PM Pool equipment area receptacle  
Anonymous
Unregistered

A home inspector notes a receptacle in the pool equipment area that does not work. The home buyer wants it fixed. Electrician arrives and discovers the receptacle was originally connected to the 220 pump circuit (which has a neutral conductor in addition to a grounding conductor). 680-6(a) says the required receptacle must be supplied by a general purpose branch circuit. I know somewhere it also prohibits tapping a dedicated circuit for another load but I can't find it. The original installation is from 1969. It would be a major job to bring another circuit in. What would you do?
Brian


Work Gear for Electricians and the Trades

#31765 - 12/03/03 10:33 PM Re: Pool equipment area receptacle  
stamcon  Offline
Member
Joined: Mar 2001
Posts: 329
So San Francisco CA
Brian, would it be possible to install a breaker panel near the pump and turn the "pump circuit" into a feeder for the new panel? Then run the pump and receptacle circuits from the new panel.

steve


#31766 - 12/04/03 08:07 AM Re: Pool equipment area receptacle  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,308
i wonder if 430.27 (or maybe something else in part 11) would help??

~S~


#31767 - 12/04/03 09:04 AM Re: Pool equipment area receptacle  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
I think this is a question about local ordinance that defines what part of existing installations must be upgraded to the most modern version of the NEC in effect for the jusrisdiction when a repair of the existing installation occurs.

The 1969 installation, arguably, was installed under the 1968 NEC which has no requirement for the convenience receptacle. The required outlet that you site as 680-6(a) wasn't introduced until the 1981 edition of the NEC, and it wasn't until the '99 NEC that the required outlet was to be extended from a general lighting circuit.

What gets grandfathered in, in this jurisdiction?

If all that is required to restore the receptacle installation to service is the replacement of the device or the repair of a conductor splice, that's what I'd do.


Al Hildenbrand

#31768 - 12/04/03 11:52 PM Re: Pool equipment area receptacle  
Anonymous
Unregistered

Sparky,
We're still using the 99 Code. 430-27 refers to ampacity of conductors between motor and capacitor. I need to get a copy of the 02 but I've been putting it off.
ElectricAL,
I believe I'm going to do just that.
Thanks, Brian



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7647 MB (Peak: 0.9008 MB) Zlib enabled. Server Time: 2017-05-27 04:17:15 UTC