splicing grounding electrode conductor #30760
10/27/03 01:57 PM
10/27/03 01:57 PM
D
donles  Offline OP
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
Does any one splice or tap to the GEC?
What do you use? I'm upgrading a duplex with 100 amp panels side by side in the basement.
Rather than run two #6 solid cu from each panel to the ground rods outside, I'd like to run from one panel to the rods. Then run #6 from the 2'nd panel and tap onto the 1'st panel's GEC using irreversible compression-type connectors. I believe this is permitted by NEC 250.64 (C) and (D).

I've checked with 2 supply houses and they evidently do not carry a compression tool or the connectors. Anyone have experience with this?

Work Gear for Electricians and the Trades
Re: splicing grounding electrode conductor #30761
10/27/03 03:09 PM
10/27/03 03:09 PM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Donles,
Burndy, Thomas & Betts, and Anderson are the ones that make the tools and materials off the top of my head. All of these can be found by a simple web search.

If you quit that solid habit, you can use a Cadweld, made by erico www.erico.com
These are reusable for a long time, and do not degrade like crimps or split bolts.

Re: splicing grounding electrode conductor #30762
10/27/03 04:27 PM
10/27/03 04:27 PM
D
donles  Offline OP
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
What is the ballpark cost for Cadweld?

I've found the cost of the T&B tools to be prohibitive for my infrequent use. Although I did see a Penn-Union tool on ebay for what is probably alot less than retail. Minimum bid $99 for a TDM-250 and the auction was winding down.

Re: splicing grounding electrode conductor #30763
10/27/03 05:01 PM
10/27/03 05:01 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I normally use a split bolt for this.

Re: splicing grounding electrode conductor #30764
10/27/03 05:26 PM
10/27/03 05:26 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Split bolts are not irreversible. Perhaps you're thinking of an equipment grounding conductor and not a grounding electrode conductor?


Ryan Jackson,
Salt Lake City
Re: splicing grounding electrode conductor #30765
10/27/03 05:37 PM
10/27/03 05:37 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
If you do a search on this site for cad welds you will find a thread that talks about one shot disposable cad welds for $5.00 I have not used them but it sounds like a great deal.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: splicing grounding electrode conductor #30766
10/27/03 06:40 PM
10/27/03 06:40 PM
D
donles  Offline OP
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
I looked at Erico's site for the one-shot, inexpensive cadweld splices. Their site isn't the most user friendly. I did come across mold # PG11L for #4 solid to #4 solid taps but no details. I'll have to call suppliers tomorrow.
Thanks.

Re: splicing grounding electrode conductor #30767
10/27/03 07:10 PM
10/27/03 07:10 PM
E
eprice  Offline
Member
Joined: Aug 2003
Posts: 64
North Logan, Utah, USA
Ryan,

Couldn't 250.64(D) be used here, and wouldn't that allow the use of something like a split bolt to make a tap to a second enclosure as long as the GEC to the first enclosure meets 250.64(C) and is not spliced where the tap joins?

Re: splicing grounding electrode conductor #30768
10/27/03 07:24 PM
10/27/03 07:24 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
EPRICE: Thanks! I got so caught up the topic starter's question of how to do it irreversibly that I didn't look at the code. Good catch.

Scott: Sorry!


Ryan Jackson,
Salt Lake City
Re: splicing grounding electrode conductor #30769
10/27/03 08:20 PM
10/27/03 08:20 PM
D
donles  Offline OP
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
Care to expand on that a little?
Meanwhile, I'll consult the code.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,890
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 20
Admin 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,830 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.048s Queries: 15 (0.014s) Memory: 1.0213 MB (Peak: 1.1965 MB) Zlib enabled. Server Time: 2018-01-18 19:56:38 UTC