#30760 - 10/27/03 02:57 PM splicing grounding electrode conductor  
donles  Offline
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
Does any one splice or tap to the GEC?
What do you use? I'm upgrading a duplex with 100 amp panels side by side in the basement.
Rather than run two #6 solid cu from each panel to the ground rods outside, I'd like to run from one panel to the rods. Then run #6 from the 2'nd panel and tap onto the 1'st panel's GEC using irreversible compression-type connectors. I believe this is permitted by NEC 250.64 (C) and (D).

I've checked with 2 supply houses and they evidently do not carry a compression tool or the connectors. Anyone have experience with this?


Work Gear for Electricians and the Trades

#30761 - 10/27/03 04:09 PM Re: splicing grounding electrode conductor  
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Donles,
Burndy, Thomas & Betts, and Anderson are the ones that make the tools and materials off the top of my head. All of these can be found by a simple web search.

If you quit that solid habit, you can use a Cadweld, made by erico www.erico.com
These are reusable for a long time, and do not degrade like crimps or split bolts.


#30762 - 10/27/03 05:27 PM Re: splicing grounding electrode conductor  
donles  Offline
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
What is the ballpark cost for Cadweld?

I've found the cost of the T&B tools to be prohibitive for my infrequent use. Although I did see a Penn-Union tool on ebay for what is probably alot less than retail. Minimum bid $99 for a TDM-250 and the auction was winding down.


#30763 - 10/27/03 06:01 PM Re: splicing grounding electrode conductor  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I normally use a split bolt for this.


#30764 - 10/27/03 06:26 PM Re: splicing grounding electrode conductor  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Split bolts are not irreversible. Perhaps you're thinking of an equipment grounding conductor and not a grounding electrode conductor?


Ryan Jackson,
Salt Lake City

#30765 - 10/27/03 06:37 PM Re: splicing grounding electrode conductor  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
If you do a search on this site for cad welds you will find a thread that talks about one shot disposable cad welds for $5.00 I have not used them but it sounds like a great deal.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#30766 - 10/27/03 07:40 PM Re: splicing grounding electrode conductor  
donles  Offline
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
I looked at Erico's site for the one-shot, inexpensive cadweld splices. Their site isn't the most user friendly. I did come across mold # PG11L for #4 solid to #4 solid taps but no details. I'll have to call suppliers tomorrow.
Thanks.


#30767 - 10/27/03 08:10 PM Re: splicing grounding electrode conductor  
eprice  Offline
Member
Joined: Aug 2003
Posts: 64
North Logan, Utah, USA
Ryan,

Couldn't 250.64(D) be used here, and wouldn't that allow the use of something like a split bolt to make a tap to a second enclosure as long as the GEC to the first enclosure meets 250.64(C) and is not spliced where the tap joins?


#30768 - 10/27/03 08:24 PM Re: splicing grounding electrode conductor  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
EPRICE: Thanks! I got so caught up the topic starter's question of how to do it irreversibly that I didn't look at the code. Good catch.

Scott: Sorry!


Ryan Jackson,
Salt Lake City

#30769 - 10/27/03 09:20 PM Re: splicing grounding electrode conductor  
donles  Offline
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
Care to expand on that a little?
Meanwhile, I'll consult the code.


Page 1 of 2 1 2

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.8157 MB (Peak: 0.9894 MB) Zlib enabled. Server Time: 2017-07-23 12:49:53 UTC