I'm doing a job and have to run PVC underground which should be 18" deep, and metal ridgid with pipe wrap at the ends where it comes out of the ground. I have seen jobs where the PVC was run up from the underground to above ground level which should be against code, even though the PVC is marked schedule 40 ridgid. I don't believe this is legal. Correct?
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
aldav53 i know of no code ref here , other than that of 'physical damage' that would dictate steel on UG surfacing.
even then, sch 80 goes a long way....
fwiw, there would be more of a focus on the grounding of an isolated sweep, either in burial depth or bonding to it.
there would also be some technicalities feeders/branch circuits vs. service entrance
so you'll need to expand a tad for us
~S~
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
They will be branch circuits from a 200a subpanel feeding a Spa, barbecue, waterfall, etc. (Using Schedule 40)
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
It is perfectly code compliant to break the surface with PVC and there are many installations in this area that do just that.
Underground Dwelling services are often done that way.
For myself I prefer to use IMC or RMC to come up out of the ground.
An isolated elbow must have all parts of it 18" below earth or be encased in 2" of concrete. 250.86 Exception No. 3
Now if only the POCO would bond their rigid pole risers we would be doing something
[This message has been edited by iwire (edited 09-27-2003).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
[brokenrecord] Check with your AHJ [/brokenrecord]
It's illegal in my community to have PVC as the "groundbreaker" - it MUST be RMC/IMC to min burial depth for the raceway or cable.
|
|
|
|
Joined: Apr 2002
Posts: 914
Member
|
This is what the NEC handbook has to say. Rigid Nonmetallic Schedule 40 and Schedule 80 PVC Conduit (DZYR) Rigid nonmetallic Schedule 40 PVC conduit is suitable for underground use by direct burial or encasement in concrete. Unless marked “Underground Use Only” or equivalent wording, Schedule 40 conduit is also suitable for above ground use indoors or outdoors exposed to sunlight and weather where not subject to physical damage. Schedule 80 conduit has a reduced cross-sectional area available for wiring space and is suitable for use wherever Schedule 40 conduit may be used. The marking “Schedule 80” identifies the conduit as suitable for use where exposed to physical damage and for installations on poles to comply with Section 352.10(F) and 352.12(C). I've never seen any underground service done with any material other than PVC. And as long as its schedule 80, it should pass anywhere.
|
|
|
|
Joined: May 2002
Posts: 132
Member
|
Agree with all above posters. Also it should state right on the PVC conduit its schedule and its limitations for usage if doubt arises during installation. The subject of physical damage needs to be taken into consideration. For services where vehicular traffic is present concrete bollards will alleviate this problem.
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
The part in the code where it says PVC can be run above ground if "not subject to physical damage" can possibly be a gray area, but tells me it cannot be run up out of the ground, should be ridgid I believe with 20ml pipe wrap.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Aug 2003
Posts: 173
Member
|
"but tells me it cannot be run up out of the ground" That is a very bold assumption. It can also be a costly one, for you.
PVC is very regularly run above ground. The subject to physical damage is just that. A service riser going up a utility pole along a roadway is subject to physical damage, we use galv. The other end of the same pipe going into the meter pan on the side of someone's house surrounded by shrubs and grass IMO is not "subject to physical damage" any more than sch 80 can ahndle.
Speedy Petey
"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
aldav53
Running PVC up out of the ground is very common.
The subject to physical damaged part is a judgment call between you and the inspector.
Take a look at 334.15(B) and you will see PVC listed as a means to protect NM and UF (334.10(4) conductors from physical damage.
If you do not like to break the surface with PVC do not do it, I do not, but it is in most cases code compliant.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|