ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 23 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#28809 08/31/03 02:49 PM
Joined: May 2002
Posts: 68
E
Eandrew Offline OP
Member
does anyone know the purpose of tie breakers in switchgear.

Lets say you have a 4000 amp tie breaker ( with a spring loaded handle) between two 3000 amp switchboard panels (each 3000 amp switchboard section housing about 600 amp feeder breakers. Why is this tie breaker connected via copper bussing in the switchgear necessary?

#28810 08/31/03 03:56 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
It is likely that the fault duty is too high for insulated cables to withstand without damage. Properly braced busbars may have been specified particularly for the increased fault current when the tie breaker is closed. The fault duty effectively doubles in that situation—with three breakers closed, two transformers are then operating “in parallel”.




[This message has been edited by Bjarney (edited 08-31-2003).]

#28811 08/31/03 08:59 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Main-tie-main switchgear is very common in critical facilities. Depending on the application, each of the mains is designed to carry half of the total swgr load on a normal day. In the event of a failure of one source, the main breaker on the "bad" source is opened, then the tie is closed for the "good" main to carry the full load of the SWGR.
Sometimes I design in a main-tie-tie-main. This allows maintenance access to either side of the tie without any live bus to contend with.


Ron
#28812 08/31/03 11:51 PM
Joined: Aug 2003
Posts: 9
W
Junior Member
In the 8 years I've been with my current company, we have used our tie breakers more than once. I think they are a good investment for a company.

We melt copper in large induction furnaces which will "freeze up" if you leave power off for too long. When a main lead blows off the 34Kv, we can tie into a secondary incoming line.


Please buy American made Winchester ammunition! Business is slowly going overseas!
#28813 09/02/03 07:47 AM
Joined: Jan 2002
Posts: 15
F
Member
At my plant we have 6 indoor substations that we can tie together in case of a xfmr failure in one of them. We have used it a couple times here in the last few years after a xfmr failure. We also use the Kirk key sytem to avoid any kind of mix up when tying subs together.