#28173 - 08/12/03 04:12 PM Phases in different raceways  
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
Hi Guys (and ladies, of course): I need a little learnin' here. A church in this area is undergoing a service upgrade. There are four separate raceways being installed to provide a three phase service. Each one, equipped with weatherhead, travels along the back side of the church building for a distance of about 50 feet before elbowing through the wall into a switchgear room. So far, the conductors for the three hot legs (color-coded black, red and blue - three conductors per leg) have been pulled into the conduits. However, unlike what I've read, and seen discussed here previously, all three black legs are in one conduit, all three reds in another, and all three blues in the third (instead of one of each appearing in each conduit). The fourth conduit is empty at present - I assume that the "neutral" is supposed to go here.

I thought that this was strictly a NO-NO, and serious problems could result from this. Can y'all elaborate on this for me?

Mike (mamills)


Work Gear for Electricians and the Trades

#28174 - 08/12/03 04:28 PM Re: Phases in different raceways  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
.

[This message has been edited by iwire (edited 08-12-2003).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#28175 - 08/12/03 04:35 PM Re: Phases in different raceways  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I have done similar installations underground but I do not believe you can do this aboveground look at the one exception for Paralleled Installations.

[quote]300.3 Conductors.

(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (4).

(1) Paralleled Installations. Conductors shall be permitted to be run in parallel in accordance with the provisions of 310.4. The requirement to run all circuit conductors within the same raceway, auxiliary gutter, cable tray, trench, cable, or cord shall apply separately to each portion of the paralleled installation, and the equipment grounding conductors shall comply with the provisions of 250.122. Parallel runs in cable tray shall comply with the provisions of 392.8(D).

Exception: Conductors installed in nonmetallic raceways run underground shall be permitted to be arranged as isolated phase installations. The raceways shall be installed in close proximity, and the conductors shall comply with the provisions of 300.20(B).

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#28176 - 08/12/03 04:38 PM Re: Phases in different raceways  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Mike,
What are raceways made of?
Don


Don(resqcapt19)

#28177 - 08/12/03 04:45 PM Re: Phases in different raceways  
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
Don;
They appear to be rigid steel pipe with threaded fittings. I'm guessing they are about 3 1/2 - 4" diameter.

Mike (mamills


#28178 - 08/12/03 04:52 PM Re: Phases in different raceways  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Don would you be able to apply 300.3(B)(3) to a paralleled installation.


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#28179 - 08/12/03 06:07 PM Re: Phases in different raceways  
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
I haven't personally seen an installation like this, but someone I know told me of a serious heat problem caused by the situation you described. Perhaps someone can elaborate on possible complications.


#28180 - 08/12/03 06:25 PM Re: Phases in different raceways  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Bob

I would say based on 300.3(B)(1)exception, that the above installation is a violation, and it will definitely cause a heating of the conduit problem. Possibly causing a fire.
300.3(B)(3) does not pertain to paralleled installations.
Even if they had run PVC above grade, that is a violation.
I understand why some like to install a parallel service this way, it makes working with the conductors easier.

Pierre


Pierre Belarge

#28181 - 08/12/03 06:45 PM Re: Phases in different raceways  
arseegee  Offline
Member
Joined: Jan 2002
Posts: 324
Statesboro, GA USA
All i can say is stand back when they throw the main. Due to the magnetic field produced from the flow of electrons, you DO NOT want to install all the same phase conductors in there own pipe. I know a company that did that on a Kwickset factory not far from me. Blew the concrete wall off the back of the building. That was their first and last big job.

[This message has been edited by arseegee (edited 08-12-2003).]


#28182 - 08/12/03 08:29 PM Re: Phases in different raceways  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Bob,
In my opinion 300.3(B)(3)would permit this installtion if the raceways were nonferous. Note that you would have to comply with 300.20(B) where the conductors enter the panel. If these are ferous raceways, then the installation is a code violation and will fail very quickly when any load is applied.

Pierre,
I see nothing in 300.3(B)(3) that says you can't use the section for parallel installations.

Don


Don(resqcapt19)

Page 1 of 2 1 2

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,138
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.8181 MB (Peak: 0.9921 MB) Zlib enabled. Server Time: 2017-05-22 15:28:29 UTC