#27872 - 08/04/03 03:18 PM Voltage Drop - 14 amps in 100'  
Rob Thacker  Offline
Junior Member
Joined: Dec 2002
Posts: 1
Chico, CA USA
I am looking at a 1650 watt water heater installed approximately 100 feet away from the breaker. In using some on-line voltage calculators available, it appears as though this branch circuit will require #10 AWG copper conductor.

Assuming these calculators are correct, the voltage drop is 4.4 % over #12 copper. I have some electricians advising that this is not correct, referring to some rather loose rules of thumb about up-sizing for runs in excess of 200 feet. "#12 AWG is fine"

I have also had it inferred that it makes a difference whether or not the load is resistive or inductive. I don't see anything about this in NEC 210-19 (using 1999). In fact FPN No. 4 explicitly includes heating loads.

Can anyone chime in here and authoratively settle the bet.


Unforgiven

Work Gear for Electricians and the Trades

#27873 - 08/04/03 03:50 PM Re: Voltage Drop - 14 amps in 100'  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
On the calculator I use 12 AWG is truly borderline with 5% drop, 10 AWG will keep you less then 3% drop.

The most recent job specs we get spec 10 AWG for 20 amp circuits longer than 75'.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#27874 - 08/04/03 05:03 PM Re: Voltage Drop - 14 amps in 100'  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
{Don’t get your panties in a bunch if this explanation is not immediately understandable but} for heaters, power factor is close the 1.0, or “unity,” so only the resistive component [er, copper size] of a circuit matters. For motors, where PF<1, the reactive component of circuit impedance figures in, so conductor spacing and ferrous versus non-ferrous versus non-metallic raceway or cable jacket has an effect on voltage drop.

Offhand, I’d be tempted to save some copper by using a 240V (over 120V) heater, but looks like 240V elements start at >2kW. Then it’s a matter of what’s cheaper—a 2-pole breaker or fatter wire. If line voltage is normal, use 12AWG for 1650 watts at 100 feet. Change in performance will be barely measurable with larger cable.





[This message has been edited by Bjarney (edited 08-04-2003).]


#27875 - 08/05/03 07:15 AM Re: Voltage Drop - 14 amps in 100'  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
On a resistive load, the effect of voltage drop will be less voltage applied to the heater load, which will reduce the total wattage of the heater.
In your case, the 4.4% voltage reduction would simply reduce your heater output to 1512 watts. On a motor load, low voltage will likely cause motor starting problems, and premature failure.
Remember that circuit components for electric heat often have to be sized at 125%, per 424.3.



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7607 MB (Peak: 0.8917 MB) Zlib enabled. Server Time: 2017-05-28 01:01:11 UTC