#27732 - 07/31/03 08:12 PM 200 amp panel upgrade  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
I am changing out a 3 phase 100 amp panel fed with #2 aluminum. It has 30 circuits and the only way to change it is to upgrade it to a 200 amp to cover the circuits since they don't make a 100 amp with that many circiuts in it anymore. They do make a 125 amp with 12 circuits or 150 amp with 24 circuits which I would have to use twins on.
The problem is, can I upgrade to a 200 amp panel with only #2 aluminum feeders?


The Golden Rule - "The man with the gold makes the rule"

Work Gear for Electricians and the Trades

#27733 - 07/31/03 08:18 PM Re: 200 amp panel upgrade  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Use a 200A panel with a 100A main circuit breaker.


Ron

#27734 - 07/31/03 08:19 PM Re: 200 amp panel upgrade  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
As far as I know, you can do this. However, check the lugs on the new 200 amp panel to make sure that the wire that you connect to them is in the listed range of acceptable wire sizes.

Also, if that #2 aluminum wire is being protected by a 100 amp breaker, change that breaker to 90 amps.


Few things are harder to put up with than the annoyance of a good example.

#27735 - 07/31/03 10:58 PM Re: 200 amp panel upgrade  
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
Tom, why do you say to change the breaker to 90? Since this is a service or feeder, not a branch circuit, the code allows #2AL for 100 amps.

[This message has been edited by Electric Eagle (edited 07-31-2003).]


#27736 - 07/31/03 11:29 PM Re: 200 amp panel upgrade  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Table 310.15(B)(6) only applies to 120/240 volt 3-wire single-phase dwelling services and feeders.

If the terminations on both ends of this #2 AL are rated for 75C the 75C column can be used which shows that ampacity as 90 amps. If the terminations on either end are only rated for 60C conductors then the 60C column must be used which shows the ampacity as 75 amps.

[This message has been edited by caselec (edited 07-31-2003).]


Curt Swartz

#27737 - 08/01/03 05:55 PM Re: 200 amp panel upgrade  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
nevermind

[This message has been edited by Electricmanscott (edited 08-01-2003).]


#27738 - 08/02/03 01:54 AM Re: 200 amp panel upgrade  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Electricmanscott, what does that mean?


The Golden Rule - "The man with the gold makes the rule"

#27739 - 08/02/03 07:45 AM Re: 200 amp panel upgrade  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I wrote something, then I read the question again. I gave the wrong info. Missed the three phase part. Anyway I would go with the 200 amp panel and back feed a breaker if the lugs can't be used. I think you will have to go with the 90 amp breaker anyway. I assume that this will be enough for the loads to be served?


#27740 - 08/02/03 12:38 PM Re: 200 amp panel upgrade  
aldav53  Offline
Member
Joined: Aug 2001
Posts: 545
Chandler, AZ USA
Ya, may have to do that. I put an amp clamp on one leg and it was drawing 80 amps, panel is maxed out. Maybe I can use a 200 amp panel without the 90 or 100 amp main since it is fused at the main disconnect.


The Golden Rule - "The man with the gold makes the rule"


Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.002s) Memory: 0.7995 MB (Peak: 0.9661 MB) Zlib enabled. Server Time: 2017-10-22 09:49:46 UTC