Anybody ever splice service cable? #27322
07/10/03 06:12 PM
07/10/03 06:12 PM
E
Electric Eagle  Offline OP
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
I've got a customer that is having a water problem entering through the service which enter the house below grade in the basement. From there they have 4 150 amp panels branching from a gutter. To solve the problem I need to rebuild the service, putting all the disconnects outside and re-entering above grade. All currect service cables are fairly new and are 4 conductor.

Can I splice each of these cables in a j-box or gutter? I can't find a code prohibitting splicing the main, I've just never had to do it.

Thanks

Work Gear for Electricians and the Trades
Re: Anybody ever splice service cable? #27323
07/10/03 06:37 PM
07/10/03 06:37 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Where is the meter in this arrangement?


Ron
Re: Anybody ever splice service cable? #27324
07/10/03 06:39 PM
07/10/03 06:39 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
If it is an underground service lateral conductor, then see 230.33.


Ron
Re: Anybody ever splice service cable? #27325
07/10/03 06:45 PM
07/10/03 06:45 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
230.46 Allows service conductors to be spliced.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Anybody ever splice service cable? #27326
07/10/03 06:59 PM
07/10/03 06:59 PM
A
arseegee  Offline
Member
Joined: Jan 2002
Posts: 324
Statesboro, GA USA
David, I had a plumber run a saw thru a 4/0 SER about three years ago. He had to move his pipes and thought it would be easier to use his 18v circular saw than a drywall saw (not a real sharp guy). Well he was VERY lucky because when he went thru the SER it was rolled where he only cut the ground and neutral. The ground was cut clear through and about 50% of the neutral conductor was missing.

The panels were between floors and repulling the entire cable was out of the question but i was able to pull a new cable to an accesible point and splice the entrance.

After a discussion with the inspector, I used a 12"x12"x4" galvanized j box with two 2" nwt (romex) connectors, a 2/0 double lug for my grounding (and bond)bolted to the enclosure and three 2 conductor Ilsco insulated tap connectors for the neutrals and hots.

A hour later i had a bill for the plumber.

Re: Anybody ever splice service cable? #27327
07/10/03 08:09 PM
07/10/03 08:09 PM
E
Electric Eagle  Offline OP
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
Thanks Guys,

The meter is outside, but inside the basement is a large can with pad locks from the poco. From there it branches to a gutter and a 3" PVC comes out the bottom of the poco can. The water leaks from a joint in the 3" pvc. It is definately a potential hazard. The homeowner thinks the poco is responsible since they own the can. I think the homeowner will ultimately have to pay to update. I really can't see why it was done this way to begin with. Also, I'm sure the conductors from the meter to the poco can are undersized, since another contractor added 2 of the 150 panels a year or so ago without a permit.

Re: Anybody ever splice service cable? #27328
07/10/03 08:26 PM
07/10/03 08:26 PM
T
ThinkGood  Offline
Member
Joined: Aug 2002
Posts: 1,081
Milwaukee, WI
Water entering the service entrance is a disaster waiting to happen...


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,592 Are you busy
180,388 Re: Forum
170,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9833 MB (Peak: 1.1347 MB) Zlib enabled. Server Time: 2018-01-22 10:11:23 UTC