#26569 - 06/15/03 04:21 PM Megging circuit breakers  
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Anyone know the scoop about how to safely meg a circuit breaker? I often wonder if all the electronics that are part of circuit breakers these days would mess up megger readings. Suppose, for example, someone wants to meg out a circuit from a supply bus bar, through a distribution panel circuit breaker, through the feeder conductors..stopping at the open branch circuit breaker. Is this a practice which might show misleadingly low resistance numbers due solely to the feeder circuit breaker's electronic trip package?
Are there limits to how high the test voltage should be? Would a 1kV test voltage mess up, or interact with the trip unit, in a 240 volt breaker?


Work Gear for Electricians and the Trades

#26570 - 06/15/03 07:09 PM Re: Megging circuit breakers  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
It’s probably a little more common to use 500VDC on 240/208V stuff. As for readings, it’s primarily a matter of experience, and comparing pole-to-pole readings for lack of any IR history. In electronic-trip molded-case breakers, if there is no external communications or relaying, the meg tests generally shouldn’t damage anything—but get your mitts on the breaker instruction pamphlet for any warnings.

Biddle sells a booklet titled “A Stitch in Time” that covers the subject in a practical manner.

Obviously, megging a VFD would be suicide.



Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7438 MB (Peak: 0.8611 MB) Zlib enabled. Server Time: 2017-04-29 15:41:09 UTC