ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Dryer, Range grounding from "Main" panel
by gfretwell. 05/24/17 09:35 PM
210.70 / Wall Switch / When adopted?
by gfretwell. 05/24/17 09:18 PM
Any UL 508 experts out there?
by sparkyinak. 05/23/17 11:04 PM
Heat pump conundrum
by sparkyinak. 05/21/17 08:49 PM
Interesting week
by HotLine1. 05/20/17 11:57 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,759 Are you busy
171,769 Re: Forum
164,706 Need opinion
Who's Online Now
0 registered members (), 73 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#26383 - 06/10/03 06:43 PM primary fusing  
drillman  Offline
Member
Joined: Mar 2003
Posts: 97
Somewhere in Texas
We had the incoming line to the complex blow a fuse yesterday. Single phased the place for over an hour until the power company got there.

My question is how are those things sized?

why do I ask? Because they are 125 amp fuses on a 7200 volt line. After changing them out the lineman measured the load it was 92 , 106 and 110. That 110 sure sounds a bit to close to me but I know next to nothing about HV stuff.

Now 125 amps at 7200 volts would be 1875 amps at 480 volts correct?

There is going to be a meeting with the power company and my engineer boss to try and solve this problem.


Work Gear for Electricians and the Trades

#26384 - 06/10/03 08:25 PM Re: primary fusing  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
The characteristics of medium voltage fuses are different than low voltage fuses. Assuming that you refer to an E style (125E) med. volt. fuse is designed to protect the down stream transformer, and can handle significantly more full load current for more time, than the equivelent situation for low voltage.


Ron

#26385 - 06/10/03 08:37 PM Re: primary fusing  
drillman  Offline
Member
Joined: Mar 2003
Posts: 97
Somewhere in Texas
I figured something like that.

The catch is there is no downstream transformer but rather downstream transformers.

Each building gets its own drop with fuses and a transformer. NONE of those blew, the main into the complex blew.

Does this make sense to the high voltage / medium voltage guys?


#26386 - 06/10/03 09:25 PM Re: primary fusing  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
As an example, 100-ampere “K” or “T” universal-link 15-38kV fuses are intended to continuously withstand their rated current, and not open at 200-240 amperes for 300 seconds. [The next standard size listed for ANSI Std C37.41 fuses is 140 amperes.] Some load balancing on the 480V side might help.




[This message has been edited by Bjarney (edited 06-10-2003).]



Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7596 MB (Peak: 0.8888 MB) Zlib enabled. Server Time: 2017-05-25 14:27:14 UTC